I recently had a discussion with another spark about induction hobs and diversity.

He pointed out that an induction hob may have, for example, 4 X 3.2kW cooking zones (total 12.8kW), but due to internal power management, the appliance could never draw more than say 7.2kW, that being shared among the zones in use. His view is that the limited maximum, in this example 7.2kW, should be the design current for the circuit, and no diversity can be applied as the maximum could easily be reached.

My conflicting view is that diversity can be applied, but should use the sum of all elements (in this example 12.8kW) for the calculation. My logic is as follows:

Take another hob, identical ratings, but this time not an induction hob, and with no power management to limit the maximum load. After diversity, it is expected to pull 24A although in theory it could pull 56A if all elements are on full simultaneously.
Compare this to the induction hob - again after diversity it would be expected to pull 24A, but due to power management could only pull a maximum of 31A, even if all zones are on full whack at the same time.

What are the views and experiences of other members of the forum on the subject?
 
Depends what part you read
VERIFICATION OF ELECTRICAL INSTALLATIONS
134.1 Erection
Regulation 134.1.1Good workmanship by competent persons or persons under their supervision and proper materials shall be used in the erection of the electrical installation, Electrical equipment shall be installed in accordance with the instructions provided by the manufacturer of the equipment.
 
Depends what part you read
VERIFICATION OF ELECTRICAL INSTALLATIONS
134.1 Erection
Regulation 134.1.1Good workmanship by competent persons or persons under their supervision and proper materials shall be used in the erection of the electrical installation, Electrical equipment shall be installed in accordance with the instructions provided by the manufacturer of the equipment.

My blue book says this, and so did my yellow one. You have quoted from an earlier version of the regs.

[ElectriciansForums.net] Diversity and induction hobs
 
Some interesting responses.

I have recently fitted a huge range cooker which had an electric hob. I worked out the max demand using the OSG diversity and it 'just' crept into using a 6mm cable. However the MI clearly said 50A supply with a 10mm cable. The 6mm on an appropriate MCB would have been fine but after being clearly told by the manufacturer that it needed a 10mm cable that was the right option.
Was that a Rangemaster? I had a similar thing.
[automerge]1583153796[/automerge]
My blue book says this, and so did my yellow one. You have quoted from an earlier version of the regs.

‘Twas in the green one that said, ‘shall be installed in accordance with’, I believe.
 
My blue book says this, and so did my yellow one. You have quoted from an earlier version of the regs.

View attachment 56101
Yes he has, I read the new regulation (new with Amd 3 of the 17th) slightly different to the old. Now we have to take the MI into 'account' which I read as the electrician having more of a choice rather than sticking rigidly to the MI as in the older regs that @Markyd has quoted from.
Was that a Rangemaster? I had a similar thing.
[automerge]1583153796[/automerge]
‘Twas in the green one that said, ‘shall be installed in accordance with’, I believe.
Yes, I think it was a rangemaster, a beast! The first time I have had to use 10mm for a cooker!
 
Do you think that is the case for all hobs, or just induction hobs?
My take is the induction hob has the potential to require a significant circuit upgrade if replacing a ceramic hob. To avoid adding a series buyer resistance (sorry) they’ve invested in the power management to bring it back to a “normal hob” maximum load.
 

Reply to Diversity and induction hobs in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
487
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
960
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
900

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top