No, that's fine - just looking for a short-term solution until finances allow for a proper resolution. Many thanks for all your help.
I know that finding ~£500 is not always easy or possible, but really
don't touch that circuit at all - disturbing it could trigger a fault which it is not adequately protected against.
Better still pull the 45A fuse and wait until it can be safely sorted.
If the circuit protection was good then no problems with advising you how to add a socket, but not when it is the electrical equivalent of an unexploded bomb.
Out of curiosity I tried to calculate what would happen if there was a L-E fault at the remote socket, making some broad assumptions on the way:
- Your supply is 230V with an impedance of 0.3 ohms, roughly split between the service live and earth (a little below the assumed worst case for TN-C-S supplies).
- You have about 30m of 2.5mm T&E with a 1.5mm earth conductor
- The fuse is a 45A one following the curves in Figure 3A1 of the 18th edition wiring regulations
This leads to the following equivalent circuit:
In the event of a fault you have a supply impedance to the end point R1 of 0.15+0.222 = 0.372 ohms, and an earth/CPC impedance R2 of 0.15+0.363 = 0.513 ohms
As a result around 260A flows and anyone touching the end "earth" would find it at 133V above the true earth potential. Assuming they have an approximate impedance of 1.875k ohm to Earth (the 50% 100V case from Wikipedia) they would get a 71mA shock, this is above the "let go threshold" so they would probably suffer it until the fuse cleared the fault.
The fuse would take around 2.25 seconds to disconnect, that puts a 71mA shock in the 5-50% probability region of causing heart fibrillation and likely resulting in death. If someone was unlucky and a bit damp, the current could be easily 50% higher and at this sort of exposure time solidly in the > 50% chance of fibrillation.
During that fault time the conductors in the T&E cable would reach about 266C, so around 100C above the short-term damage level. So even if no one is electrocuted, and no bad connections to create higher temperature hot spots, the whole circuit (and possibly any bundled with it on route) would have to be rewired.
If you re-run the calculations with 0.8 ohm supply impedance, the upper 5% or so of a TN-S supply (which yours looks a bit like from the photo), then you get around 166A flowing and a resulting disconnection time of around 35 seconds. As a result the 2.5mm T&E's CPC conductor would reach a temperature of around 623C, most likely starting a fire.