You are probably aware of these Forms A, B and C on the MCS site:
Microgeneration Certification Scheme - Heat Pumps
which we have to complete prior to connecting a heat pump.

I want to put the application in early on one of my jobs because it is a largish heat pump and in a village and I want to know early if network reinforcement is required.

A stuff of a lot of detail on power quality harmonics, voltage fluctuation and flicker is required. I got straight through to someone sensible at Kensa who is filling it in and sending it back. Nibe just puts me on hold with muzak so have sent a request to an anonymous 'info@...' email address.

Where is everyone getting this info. I cannot believe all these forms are being done individually by the manufacturers. Have any of the other masnufacturers already published the data?
 
EN 61000-3-2 and EN 61000-3-3 can only apply to equipment below 16A per phase. So for instance a Kensa single phase 16 kW twin compressor heat pump operates with a running current well above 16 A. Therefore EN 61000-3-11 and EN 61000-3-12 apply to it and all the detail is required.

That's how I read it anyway.
 
From Form A
Use this form to apply to connect new or additional heat pump equipment rated up to 75A per phase that complies with two specific standards that cover power quality – EN 61000-3-2 and EN 61000-3-3
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

BruceB

Arms
-
Joined
Location
Bath/Bristol
What type of forum member are you?
Retired Electrician

Thread Information

Title
DNO application to connect for heat pumps
Prefix
N/A
Forum
Solar Thermal Advice Forum
Start date
Last reply date
Replies
3

Advert

Thread statistics

Created
BruceB,
Last reply from
jason121,
Replies
3
Views
6,424

Advert

Back
Top