Hi All,

I need to change a DB in a block of flats in central London (W2 postcode), where EDF can't give a date for at least 6 weeks to come and isolate the supply, but at the same time won't / can't give out a date after this, which makes no sense to me!
This is both options of just popping around and isolating until work is done or installing a smart meter with DP switchgear!
The supply is a standard 1361 Type II fuse, and i'm not too keen on cutting the tags!

Does anyone have alternative methods of isolating the supply so as to change the DB? Also what is the average cost nowadays for this?

TIA
 
I don’t think I have ever met or worked with a sparks who have waited for the supplier to remove the cutout fuse,

the only jobs where the supplier has been needed to come to site is to either move a meter or replace a busted head

I hope your not implying that people cut the sacred seals on DNO cut outs ??
[automerge]1597102316[/automerge]
Hi All,

I need to change a DB in a block of flats in central London (W2 postcode), where EDF can't give a date for at least 6 weeks to come and isolate the supply, but at the same time won't / can't give out a date after this, which makes no sense to me!
This is both options of just popping around and isolating until work is done or installing a smart meter with DP switchgear!
The supply is a standard 1361 Type II fuse, and i'm not too keen on cutting the tags!

Does anyone have alternative methods of isolating the supply so as to change the DB? Also what is the average cost nowadays for this?

TIA

You’ll find a list of DNO’s here


These are the people you need to contact and not your energy supplier.

It’s becoming increasingly common for DNOs to have approved contractors who can install isolators for a small fee (it’s about £60 but will probably next £1000’s in London).
 
Supply is in a communal alcove in the basement (under the pavement). 3-Phase in and about 1.5mtrs away split into 4no BS1361 Type II Fuses (Landlord, Flat 1,2,3), another 1mtr away is EDF meters before heading off to each flat. In each flat adjacent to the DB is a metal junction box before entering the DB.

Is there not any OCPD installed after the meter to protect the cable running to the flat?

What type of cable is running to the flat and how is it installed?
 
Is there not any OCPD installed after the meter to protect the cable running to the flat?

What type of cable is running to the flat and how is it installed?
Most definitely not if it’s the older flats then there will be a BS 5419 isolator so many permutations with this type of install, need a lot more detail to help the guy out
 
cbuk2k2 , I would never advocate removing the seals :rolleyes:

likwise would not advocate buying a big pack of meter seals off eBay for 4.99 so to redo Z removed seals so it looks like the fairy never came

(you can even buy genuine seals and re-sealing tool off x meter fitters off eBay)
 
I'm having a battle with UK power networks and the customer's energy supplier. neither wan't to take the responsibility for pulling the fuse. UKPN say it's the energy supplier and visa versa. It's looking like the seal fairy is going to make a visit.
 
Why do you say most definately not?
Most of these installs just have the DPI covering the cable to flat like I said BS5419 on the older installs or 60947-3 on the newer installs.
[automerge]1597266625[/automerge]
I'm having a battle with UK power networks and the customer's energy supplier. neither wan't to take the responsibility for pulling the fuse. UKPN say it's the energy supplier and visa versa. It's looking like the seal fairy is going to make a visit.
That seal fairy saves a lot of time for the electrician carrying out the work never had any issues previously so do what you gotta do mate
 

Reply to DNO Isolation For Changing DB in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
257
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
739
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
721

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top