Guys, can I ask you all to reply to this thread with details for each DNO that you have had dealings with and their approach regarding the G83 16A limit - plus any info if you have seen that this has changed over time.
The ENA have confirmed that the correct value to use for the G83 limit is the inverter output figure and NOT the kWp for the panels but I have heard that some DNOs are using the wrong value. So I'd like to gather the info of who is doing what.
I will use this to go back to the ENA in order to find a way to get all DNOs to work on the same, correct, basis.
This is going to become more important as it appears DNOs (I've heard of SSE and WPD) that are now strictly enforcing the 16A limit and requiring anything larger to be handled under G59 - with associated cost implications.
The ENA have confirmed that the correct value to use for the G83 limit is the inverter output figure and NOT the kWp for the panels but I have heard that some DNOs are using the wrong value. So I'd like to gather the info of who is doing what.
I will use this to go back to the ENA in order to find a way to get all DNOs to work on the same, correct, basis.
This is going to become more important as it appears DNOs (I've heard of SSE and WPD) that are now strictly enforcing the 16A limit and requiring anything larger to be handled under G59 - with associated cost implications.