bill.birch
SSE install their own REC 4 isolator after the service cut out / polyphase meter on split phase. Two ways are used as L1 and L2, L3 is blanked off and the neutral is a solid non switched link. They will fit a "normal" REC 4 but will not be held responsible for any damage caused to the system if the neutral breaks first or makes last - their view is that the consequencies however small of getting momentary - or worse - 460V to earth (in a 230-0-230 tncs system) is too great to risk. I had a Hager 63A type D 3way mcb to isolate the split phase supply from a wind turbine i.e. L1, L2, neutral but since that "discussion" I have taken the neutral to a common neutral bus connection inside the mcb enclosure.