Hi guys, first post on here so hope it doesn’t sound too dull. I’ve recently qualified but my background is domestic...recently started with a company working in commercial so haven’t had much experience in working with contactors. But basically I’ve got 3 rows of lights that need to be separated with individual switches as they are all on together at the moment..what I can’t get my head Around is if I use a 3phase contactor with my switch wires coming in to energise the coil won’t that effectively turn the contactor on so all 3 of my loads become live? Do I need to have separate coils like 3phase coil or separate contactors?
 
A contactor is an electrically controlled switch, you will need one for each load you want to control.
Power >> switch >> contactor coil
Power >> contactor line terminal || contactor load terminal >> lights
 
If you currently have 3 phase going to the 3 lines of lights and you want to turn on each line individually then you will end up using 1 phase per line of lights. Single phase. As above, each switch will switch on its own contactor, so the contactor will be single phase.
 
Most Manufacturers do a single module contactor rated at 20A however they are only 230V coils so you will need a Neutral across A2 and a feed from each switch to A1 let me know if want a drawing..
 

Reply to Do I need a 415v coil contactor? in the Lighting Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
444
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Good point they may well have put the control through a main contact.
2
Replies
20
Views
776
You only need to switch the lines and the contactor is rated per pole so for example a 16A four pole contactor would be fine.
Replies
1
Views
317

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top