I am just changing my plug top oven over & gas hob and noticed the following:

32AMP Breaker > 6MM Cable > Cooker Switch 45a > 4mm cable > Double Socket which powers both.

13a Plug Top Oven replacing the previous same plug top. Gas Hob and just powers the igniter.

Is this right or do i need a sparky in to replace this?

Thanks in advance!
 
The precise pernickety jobsworth answer is that whether the 4mm is ok between the isolator and the socket depends on the construction of the wall and how the cable is run. The rating for that cable varies between 17.5 and 37 amps depending on this!

BUT In reality you know exactly what the loads are, and they won't be changing once the new oven is installed, and the circuit is perfectly adequate for the loads even in the worst case scenario of the 4mm being surrounded by insulation in a stud wall.
I'm assuming the gas hob has a 3 or 5 amp fuse in the plug.

As far as you are concerned there is a double socket there that you have no reason to believe isn't to regs, so use it!
 

Reply to Do I need an electrician in? 32amp to Cooker Switch to Double Socket. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
Can to OP clarify if this extension is just another room on the side of the building (so multiple cables going through the walls for lights...
Replies
6
Views
735
  • Question
Thank you for fast response. The reason I asked is because I had read elsewhere online: "Electric ovens have a wattage rating that tells you how...
Replies
2
Views
1K
  • Question
They need to put in a suitable test facility. This should have been part of the design putting in two separate circuits suggests they are not...
Replies
10
Views
3K
Check the clearance between the back panel and/or terminal cover that you've removed. Look for small burn marks.
Replies
3
Views
359
  • Question
Obviously not a building/DIY forum so will keep it short but yes - we've taken all the floors up. Several joists in the bathroom need doing as...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks