Hi Guys,

I am just changing my plug top oven over & gas hob and noticed the following:

32AMP Breaker > 6MM Cable > Cooker Switch 45a > 4mm cable > Double Socket which powers both.

13a Plug Top Oven replacing the previous same plug top. Gas Hob and just powers the igniter.

Is this right or do i need a sparky in to replace this?

Thanks in advance!
 
The precise pernickety jobsworth answer is that whether the 4mm is ok between the isolator and the socket depends on the construction of the wall and how the cable is run. The rating for that cable varies between 17.5 and 37 amps depending on this!

BUT In reality you know exactly what the loads are, and they won't be changing once the new oven is installed, and the circuit is perfectly adequate for the loads even in the worst case scenario of the 4mm being surrounded by insulation in a stud wall.
I'm assuming the gas hob has a 3 or 5 amp fuse in the plug.

As far as you are concerned there is a double socket there that you have no reason to believe isn't to regs, so use it!
 
agree with above. plug and play. once you got the hang of it.let 'erindoors have a go. then you may need an electrician.🤣😘
 

Reply to the thread, titled "Do I need an electrician in? 32amp to Cooker Switch to Double Socket." which is posted in UK Electrical Forum on Electricians Forums.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Daily, weekly or monthly email

Thread starter

Joined
Location
UK
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Trainee Electrician

Thread Information

Title
Do I need an electrician in? 32amp to Cooker Switch to Double Socket.
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
2
Unsolved
--

Thread statistics

Created
HoneycombEchoRomeo,
Last reply from
telectrix,
Replies
2
Views
2,613
Back
Top