I'm a trainee and have had two conflicting opinions from my tutors about this question so I'm hoping to elicit the benefit of your combined experience.
I've bought an old house with very old electrics. The earthing arrangement is TN-S with the main earth clamped onto the sheath of the incoming supply cable. One tutor tells me that I have to convert it to a TT system and the other tells me there are special spring loaded clamps that conform. So my question is a) do I really have to change it (I think the answer is yes) and b) which tutor is right?
A ring to the DNO is the first point of call. If TN-S is available why someone would convert it to TT is beyond me. However if TN-S or TNC-S is unavailable TT may be needed although unlikely.
And yes there are proper clamps, BS951 clamps can crush the cable.
Fabulous, thank you! The "TT" tutor gave me the impression the DNO would charge an arm and a leg. I would much prefer that option. Thanks for your help.
Round our way Northern powergrid charge around ÂŁ165 for a PME/TN-S connection onto existing service cable where they do not have to make the cable dead at the breach joint in the road.
This is the route I direct all my customers to as for me to provide a TT with similar values would cost them more. A TT with poorer values would be cheaper, but I never like to use RCDs as primary fault protection where there is a reasonable alternative.
Got a picture of the cable and clamp? It is either a proper DNO clamp or a bodged up TN-S with a BS951.
[ElectriciansForums.net] Do I need to convert to TT?
I've managed to attach them but you may need to lie down to view!!
  • [ElectriciansForums.net] Do I need to convert to TT?
Could do with a close up of the clamp itself. It doesn't look like a BS951
I was thinking that too. It certainly doesn't look like any of the DNO sheath clamps I'm familiar with, but that doesn't mean it's not safe and legit.
I would be looking at the value of Ze and whether or not it was a secure and undamaged connection. It may be fine for continued use. The DNO might even come and have a free look at it to verify it.
Reply to Do I need to convert to TT? in the UK Electrical Forum area at ElectriciansForums.net
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
You need a CT clamp at main tails, it depends on the rules where you are - you used to be allowed wireliss ones (such as MyEnergi Harvi), these...