Hi,

I'm a trainee and have had two conflicting opinions from my tutors about this question so I'm hoping to elicit the benefit of your combined experience.

I've bought an old house with very old electrics. The earthing arrangement is TN-S with the main earth clamped onto the sheath of the incoming supply cable. One tutor tells me that I have to convert it to a TT system and the other tells me there are special spring loaded clamps that conform. So my question is a) do I really have to change it (I think the answer is yes) and b) which tutor is right?

Thanks
 
Phone the DNO and get the, out to maintain their earthing connection in accordance with the ESQCR.

Then find a new tutor who will teach you facts instead of attempting to teach you their opinions


Sent from my iPad using Tapatalk
 
[ElectriciansForums.net] Do I need to convert to TT?
Ive shed a bit more light on it ...
 

Reply to Do I need to convert to TT? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
391
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
975
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
958
  • Question
You need a CT clamp at main tails, it depends on the rules where you are - you used to be allowed wireliss ones (such as MyEnergi Harvi), these...
Replies
14
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top