(Rented property) The current bonding under the sink is 6mm - the electrician said it has to be min 10mm in order to pass the EICR.
Is this correct? It looks like the wire has been there since the house was built and electrician said he would have to take a new one from the fuse box and somehow get this under the sink (go through ceilings etc as fuse box font of house and kitchen is at the back)
Is this correct? Any advice would be much appreciated!
 
electrician is talking rubbish. if the 6mm bonding is intact and shows no sign of thermal damage, then it's fine to stay. a new installlation to today's regulationswould be done in 10mm.

it's like failing MOT on a pre 1965 car for no seatbelts.
 
It could be the incoming water service pipe enters the property under the sink (clouding his judgement), but as long as the existing 6mm is continuous and as #3 shows no signs of thermal damage, ..........No doesn't need replacing for satisfactory EICR.
 
electrician is talking rubbish. if the 6mm bonding is intact and shows no sign of thermal damage, then it's fine to stay. a new installation to today's regulations would be done in 10mm.

it's like failing MOT on a pre 1965 car for no seatbelts.
Thank you - even if it is on the water pipe? 6mm will pass the EICR?
 

Attachments

  • [ElectriciansForums.net] Do I need to upgrade my earth bonding under my sink to pass EICR?
    earth wire.jpg
    38.8 KB · Views: 57
It could be the incoming water service pipe enters the property under the sink (clouding his judgement), but as long as the existing 6mm is continuous and as #3 shows no signs of thermal damage, ..........No doesn't need replacing for satisfactory EICR.
Thank you for response - I have attached a picture -
 

Attachments

  • [ElectriciansForums.net] Do I need to upgrade my earth bonding under my sink to pass EICR?
    earth wire.jpg
    38.8 KB · Views: 56
Thank you - even if it is on the water pipe? 6mm will pass the EICR?

Assuming that the reason for the "issue" is purely the size, and not its location or integrity that is in question, that's fine.

Refer them to page 18 of the Best Practise guide:

https://www.----------------------------/media/1200/best-practice-guide-4-issue-4.pdf

Non-compliances with the current edition of BS 7671 that do not give rise to danger and do not require reporting:

Inadequate cross-sectional area of a main protective bonding conductor provided that the conductor is at least 6mm and that there is no evidence of thermal damage.

It should be shortly after the main stopcock, or as soon after the pipe enters the building as practicable, and before any pipework junctions, which isn't clear in your picture...but the size is certainly not a reason to fail an EICR.
 
could do with seeing where the main stop tap is in relation to the bond. anothe rconsideration is whether the water comes in in metal piework ot plastic.
 
Assuming that the reason for the "issue" is purely the size, and not its location or integrity that is in question, that's fine.

Refer them to page 18 of the Best Practise guide:

https://www.----------------------------/media/1200/best-practice-guide-4-issue-4.pdf

Non-compliances with the current edition of BS 7671 that do not give rise to danger and do not require reporting:

Inadequate cross-sectional area of a main protective bonding conductor provided that the conductor is at least 6mm and that there is no evidence of thermal damage.

It should be shortly after the main stopcock, or as soon after the pipe enters the building as practicable, and before any pipework junctions, which isn't clear in your picture...but the size is certainly not a reason to fail an EICR.
Thank you! I do not think the stopcock is under the sink... I attached more photos - thoughts?
 

Attachments

  • [ElectriciansForums.net] Do I need to upgrade my earth bonding under my sink to pass EICR?
    IMG_0570.jpg
    63.7 KB · Views: 31
  • [ElectriciansForums.net] Do I need to upgrade my earth bonding under my sink to pass EICR?
    IMG_0571.jpg
    59 KB · Views: 45
the stop tap may be at the bottom of thet vertical cold water pipe, or could be off to the left of pic.either way you need to find it if only to be able to isolate the water when you get a leak.
 
This appears to be the pipework to metal sink bonding that's no longer even required. Even if it was still required, 4mm2 would be adequate.
The main stopcock may or may not be just out of sight, but this connection would not be correct for a main incoming water bond, since the clamps are after the first branch.
 
Where is the metal sink?
Looks like a G/Y (Main Bond) coming through the top slot in backboard presumably from the MET to the hot and cold pipes.
Ooops! On closer inspection of the pic., the bonding tab on the 'sink' might well be a wire emerging through a slot in a board.
Clamp's still in the wrong place.
 

Reply to Do I need to upgrade my earth bonding under my sink to pass EICR? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
257
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
739
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
721

Similar threads

Definitely, although most likely within the accessories. I've often found that once accessories are disconnected the cabling IR is fine. Sometimes...
Replies
19
Views
2K
  • Question
Doesn't need to be right now - within a month would be OK. I have tenants at the house, but they are really friendly and helpful.
    • Like
Replies
2
Views
872

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top