Do i still need to add a switch fuse?

HappyHippyDad

-
Esteemed
Arms
Supporter
The cut out fuse is 60A.
The new CU is over 3m away.
I'm not going to be putting a fuse <60A in a switch fuse.
I'm not too sure what to do?
Nothing?
Get DNO to up main fuse to 80?
 
As I understand it, omitting an OCPD on the consumer's side in this situation is a non-compliance. However, two identical fuses in series like that, bit pointless. Also, I think you don't get full selectivity between 60A and 80A fuses under fault conditions (I might be wrong on that though, can someone confirm?).

BPG4 does not code this assuming Zs is ok, and has has it as 'NC'. To quote, "NC only. A non-conformity with BS 7671 which does not give rise to danger and where improvement is not recommended and is not required to be recorded on an EICR."
 
The cut out fuse is 60A.
The new CU is over 3m away.
I'm not going to be putting a fuse <60A in a switch fuse.
I'm not too sure what to do?
Nothing?
Get DNO to up main fuse to 80?
Just match the cut out fuse size.

efixx did a video on this and Lewden do a Switch Fuse specifically for this scenario

100A DP Fused Switch
Includes 63A, 80A & 100A fuses (22 x 58 IEC 60269-2).
New & improved range.
Extra wiring space.

Comes with 3 fuses to match the 3 standard domestic cut out sizes.
 
Just match the cut out fuse size.

efixx did a video on this and Lewden do a Switch Fuse specifically for this scenario

100A DP Fused Switch
Includes 63A, 80A & 100A fuses (22 x 58 IEC 60269-2).
New & improved range.
Extra wiring space.

Comes with 3 fuses to match the 3 standard domestic cut out sizes.
I've just watched the efixx video, there was no mention of what to do when you have a 60A fuse in the cutout. They just showed the standard 63A, 80A and 100A fuses.
 
I've just watched the efixx video, there was no mention of what to do when you have a 60A fuse in the cutout. They just showed the standard 63A, 80A and 100A fuses.
Match the 63a in the cut-out and locate the switched unit as close to the CU as practical without going over the 3 mtr tail rule.
 
If you know its a 60A in the cutout change it to 63A and put 60A in the switch fuse selectivity met. lol
That's actually a really good idea Dave.
Of course I won't do it because we can't remove the fuse :D
 
Given that in most cases we don't actually know what size the cutout fuse is (unless we pull it and check), and it's subject to change by the DNO, then I'd select the fuse in the switchfuse to suit the extended tails/SWA or whatever.
Chances are you'll never achieve selectivity on a short circuit anyway.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Advert

Thread statistics

Advert

Back
Top