I have been giving revision papers for my fault finding exam tomorrow. Here is one of the questions that i dont get. "How would you check shock protection of an MCB?" I was thinking MCB's dont provide shock protection, they just protect the circuit conductors! I know an RCD provides shock protection though? I would be suprised if at level 3 stage i had got this wrong or it was just a typo i dont know.. And how do you check for shock protection of an MCB?
 
RCDs are "additional protection" and are not always a requirement.

To check the shock protection of an MCB means ensuring Zs is sufficiently low enough so that enough current flows to operate the MCB in the required time in the event of a fault.
 
It's shock protection if it trips below 40ms. A circuit at greater than 32A will have a max disconnection time of 5 seconds, because it is most likely a distribution cct, or a larger item of equipment.
 
RCDs are "additional protection" and are not always a requirement.

To check the shock protection of an MCB means ensuring Zs is sufficiently low enough so that enough current flows to operate the MCB in the required time in the event of a fault.

Chers JUD!
 
as we no for a 32ma rcd needs to trip under 40ms what is the value for x1 generally when i do my tests it trips in 18ms to 28ms but is there a max value for x1 or is it ok if it trips in under 40ms
 

Reply to Do MCB's provide shock protection? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
316
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
841
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
964

Similar threads

Well yes obviously, but if the transformer is indoors and your lights are 50m down the garden then it's very easy to need pretty big cables at...
    • Like
2 3
Replies
42
Views
2K
  • Question
I went to look at a job like this a few years ago. My customer had a rental house, where there was an upstairs bedroom that had a newly built stud...
    • Informative
    • Like
2
Replies
15
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top