Do you have to protect submain if wired in SWA? | on ElectriciansForums
Discuss Do you have to protect submain if wired in SWA? in the Australia area at ElectriciansForums.net
R
rosewood
Hi Guys,
Sorry title should have been 'do you have to protect a submain with an rcd if wired in SWA?'
Please excuse me if this has already been asked but i cant find a straight answer to question...
I need to change a fuseboard for a split load board (2x 30ma 63amp RCD's). off this board there will be a sub main to a garage split load board which feeds some stables and a barn etc.
The board i have to change is already got 3x32a circuits and 4x6a circuits (re-wireable fuses). If i change it to a new 17th board where the main RCD's are 63amp can i still put a 63amp mcb on this board (protecting 16mm SWA to garage buried 600mm)?
No, as long as the installation is TN, and not TT.
SWA is one of the cable types (in fact all bar one of them) listed in 522.6.6 (522.6.100 in new money) as being one of the acceptable methods for additional protection.
Hi Guys,
I have to ask, ....why do you need a 16mm cable to supply a garage??
The other thing is you can't have a 30mA RCD protecting the sub-main at the main CU and another 30mA RCD at the garage. there will be no discrimination between the two. Supply the sub-main with a non RCD'd MCB....
Thanks guys,
Engineer54, the garage board will be a 10way split board feeding 4 ring mains, 3 lighting and a radial (and allowed a bit more for extras they might have in the future)
That was my way of thinking but then the sub main is not protected by an RCD? or is this acceptable?
Thanks in advance
The SWA sub main does not need an RCD because it has an earthed covering as in 522.6.6.
63A is a very high load for a barn and stables. Have the circuit coming from the house as a non RCD protected way and have a 30mA RCD at the termination in the barn.
(oops too slow)
its a bit of both believe it or not...
The swa feeding the main board uses the steel armoured for the earth but they have also put a stake down obviously because the reading wasn't good enough.
Richard burns, tahst what i cant get my head around...all the circuits in the garage add up to more than 63a (obviously thats not what is going to be pulling) but what determines the size of the breaker protecting the sub main then?
This book...Electrical Installation Design Guide: Calculations for Electricians and Designers - IET Electrical
It's fab.
Thanks guys,
Thanks in advance
I would suggest you recalculate your sub-main loads From what your implying, if you have a 100A DNO main supply, your leaving less than 40A to cover the house loads??
I don't think your going to need anywhere near 63A for this sub-main's distribution loads. Think ''diversity'' and i reckon that a good 50% of that badly calculated load will just disappear, or i'll eat my straw hat!! ...lol!!!
That would be the design current (Ib) after diversity is taken into account for the garage in this case, as your OCPD 63A (In) => Ib
too slow
I think i'm pretty dammed safe this time...lol!! I don't normally come out with such statements, but i'm sure that a garage a small stables and a barn won't draw anywhere near 63A amps. Not unless there are some pretty big KW guzzling equipments that he hasn't mentioned.
Reply to Do you have to protect submain if wired in SWA? in the Australia area at ElectriciansForums.net
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
By retired electrician, I mean that I have retained my ticket but no longer do installation work. Thanks for the clarification. I missed that it...