Main bonding is to the supply pipes.
Equipotential bonding is between copper pipes at a bath etc.

So the answer is no.

Check the gas isn’t copper pipe inside a plastic coating. (Yellow)
 
Do you need cross bonding. Main gas and water incoming is plastic and all circuits are on RCBOs
You don't and sect 4 of BS7671 is clear on that. There is a problem as sect 701 covers bathroom and one of the 3 requirements for no cross bonding is that the exp cond such as pipes are
Main bonding is to the supply pipes.
Equipotential bonding is between copper pipes at a bath etc.

So the answer is no.

Check the gas isn’t copper pipe inside a plastic coating. (Yellow)
Ok I am learning so excuse my ignorance. It really confuses me because 701 re bathroom states bonding between extraneous parts and conductive parts can be omitted if extraneous parts such as pipes are bonded. If all services come in are plastic can this be ignored??? Section 4 does say no need to bond pipes that come into premises plastic.
 
It really confuses me because 701 re bathroom states bonding between extraneous parts and conductive parts can be omitted if extraneous parts such as pipes are bonded. If all services come in are plastic can this be ignored???
Short answer - yes.

If the pipework isn't extraneous where it enters the property (because of plastic incoming), then it's unlikely to become extraneous within the property. So the pipes in the bathroom are not extraneous parts.
 
Short answer - yes.

If the pipework isn't extraneous where it enters the property (because of plastic incoming), then it's unlikely to become extraneous within the property. So the pipes in the bathroom are not extraneous parts.
Working in an industrial building the other day…all MBPC in place but not correct sizes, been like it for years
New REC supply upgrade… the water incomer is plastic so no MBPC…
The gas supply is plastic externally then from there is metallic pipework entering the building no MBPC required…
 
Short answer - yes.

If the pipework isn't extraneous where it enters the property (because of plastic incoming), then it's unlikely to become extraneous within the property. So the pipes in the bathroom are not extraneous parts.

Working in an industrial building the other day…all MBPC in place but not correct sizes, been like it for years
New REC supply upgrade… the water incomer is plastic so no MBPC…
The gas supply is plastic externally then from there is metallic pipework entering the building no MBPC
Is there anyway of knowing for sure that Gas pipe is non metallic. Someone is a previous post was saying can be plastic on outside.
 
Just have to find where the gas pipe terminates into a meter or a valve or something.
You will see if the plastic is cut off to the copper, or it won’t if it’s plastic fittings.

It might even say on the pipe itself.


Personal experience, I don’t think I’ve seen just plastic pipe going into a property, even large factories. Has always been plastic coated copper, or bare metal. (Copper or otherwise)
Someone will no doubt correct me, but I think wholly plastic is reserved for gas mains network
 
Just have to find where the gas pipe terminates into a meter or a valve or something.
You will see if the plastic is cut off to the copper, or it won’t if it’s plastic fittings.

It might even say on the pipe itself.


Personal experience, I don’t think I’ve seen just plastic pipe going into a property, even large factories. Has always been plastic coated copper, or bare metal. (Copper or otherwise)
Someone will no doubt correct me, but I think wholly plastic is reserved for gas mains network
Yes just checked. It's yellow coloured 25mm plastic to a cut off valve. The valve is metallic.only after valve everything appears metallic ie copper. They don't make it easy.
 

Reply to Do you need cross bonding in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
956
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I like your way of thinking.
Replies
6
Views
626
loz2754
L
  • Question
Any metalwork connected to the MET could rise in voltage compared to true earth under an open supply neutral fault (on TN-C-S), and that would...
2
Replies
24
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top