Just replace each rcbo with a large nail or tin foil then you will not have to do the rcd test on them and there will be no nuisance tripping.
But seriously i think the bloke who told you that needs to think about it for a few seconds. You dont even need bs7671 on this one. Just common sense.
You need to check each residual current device to see if it trips in the allotted time. An rcbo is a separate device. Well done you for not just taking it as gospel and coming on here with a 'i'm sure this aint right' attitude. You will go further than your mate in life.
At the risk of sounding like a bit of a conspiracy theorist - QUESTION EVERYTHING PEOPLE TELL YOU!!
Reply to Do you test every RCBO? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
If they are standard RCBOs the MCB aspect could be b,c, or d , but the RCD aspect is almost certainly 30mA instantaneous. If the MCB aspect...
Why go to the trouble of adding another cable, which I assume would follow the same route as the other ?. Why not upgrade it. It was to try to...