sw600

-
Joined
Oct 2, 2017
Messages
4
Reaction score
0
Location
london
Hi all

I have just bought an old house. At some point in the past someone moved the meter and consumer unit from their original position next to the incoming head (?) to about 8m away, using pyro cable. There is also a 60A fuse next to the meter. I don't know what size the fuse in the head is yet, as this is handily boxed in behind some plywood. I assume this move wasn't entirely legal.

Now I need to uprate everything to 100A for a new shower, but UK Power Networks have washed their hands of this by claiming that they can't uprate the cabling between their head and the other fuse/meter/CU, and that I should get an electrician to do it, before they can fit a 100A fuse. I called a reputable electrician and he said he wouldn't touch it. He gave me the number for a less reputable electrician who will do it, but I want to ensure that he is doing something safe, if still not entirely legal.

What should I do here? Should UKPN be doing this instead? Or even my electricity supplier's engineer?

thanks

Dan
 
I can understand both opinions.
UKPN have not authorized the original move of the meter, so why should they have to pay for the new cable.
Electricians are not meant to to any work before the main meter.
Have you asked UKPN for a quote, to see how much they will charge for the work?
 
Should be a simple job as I had the same situation in my flat rebuild, the head terminated in a neighbours flat below (old 70's conversion) my sparks ran an armoured from there to the new meter position and all was fine, where in London are you?

Oh and fit a proper shower.
 
Yes, some pics please.
Painfully Interestingly, your supplier of electricity own the meter and we are not permitted to break the seals on the meter to attach the new cables you will require.
 
Sounds like a job done before privatisation. The tails from the cut out to the meter are normally the suppliers problem not the DNO. But most suppliers only seem interested in renewing tails a short distance. I would contact the supplier and get the meter put back next to the cut out and ask for an isolation switch. The tails from the isolation switch to the consumer unit are your problem/ electricians.
 
Sounds like a job done before privatisation. The tails from the cut out to the meter are normally the suppliers problem not the DNO. But most suppliers only seem interested in renewing tails a short distance. I would contact the supplier and get the meter put back next to the cut out and ask for an isolation switch. The tails from the isolation switch to the consumer unit are your problem/ electricians.
Funny but I only noticed when I renovated my flat that the Pyro went to the CSU and the main fuse was in a cupboard next to the head in the flat below.

I think in a lot of these scenarios as you say was before privatisation and happened a lot where houses where converted in to flats, can't imagine the younger sparks being able to terminate a PYRO.
 
Thanks all for the replies. I forgot to mention that my supplier (Bulb) also refused to get involved. UKPN have refused to do the work, and would not quote.

I had been wondering about the seals, since presumably only UKPN can open up their head, and only Bulb can open up the meter, so how does anything ever get done without at least two parties there simultaneously?

I like the idea of moving the meter, perhaps I ca re-phrse it in those terms to Bulb. But aren't you supposed to limit meter tails to 3m?
 

Reply to Dodgy meter move, how to fix? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
488
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
962
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
901

Similar threads

  • Question
I agree no benefit in having it at the Db.
2
Replies
15
Views
633
Yes the first bit is just standard wiring, TNS lead cable into cut-out, cut-out to meter, meter to DP isolator, top of isolator is sealed as per...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top