Hi lads

been doing a small job for a builder and this included moving programmer + stat small distances. the programmer was moved a foot upwards and i didnt disconnect anything apart from the feed because i was feeding it from a new spur (had been a grid switch). anyhow today i re-energized the heating after it had been off for a week and now the heating doesnt work, the hot water is fine. could it be the programmer that is faulty ? it has been lying around for a week and might have taken a knock. it is a lifestyle LP522. im ok with wiring central heating from scratch but am a bit of a amateur when it comes to fault finding. there is no power reaching the stat so this means the pro is not requesting heat. can i bypass the programmer to test it by putting the central heating 'on' with perm feed ?

thanks is advance !
 
Find which cable goes into the programmers "HTG" terminal on the back, use your voltmeter to check between that terminal and neutral, should read 0 volts with heating off on programmer, 240 with heating on i.e press override on programmer, you may have to open the JB to test the cable at that end as the programmer has to be on its base to work!
 
That sounds like it could be the cause, but make sure all the links are in the terminals within the programmer (if required). Also as Somerset has mentioned above, if you can get to the connection box test the cables from the programmer and to the stat as there maybe damage between the two, what with building work on-going etc.

You both beat me to it :)
 
Last edited:

Reply to dodgy programmer in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
285
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
789
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
810

Similar threads

  • Question
Hi Gingerrubix, The fact that your previous Tenant replaced a faulty socket plate which he used for an external EV, raises an eyebrow. Also your...
2
Replies
25
Views
3K
  • Question
What attracts me is, i enjoy working in trade i like keeping busy an grafting an getting to be proud when a job is finished, with the electrician...
Replies
3
Views
387

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top