Darkwood

Right ... Just been nudged to set this up by Paul.M and sounds a good idea following recent threads I've done in the Arms..

Rules....No Offensive material... edit if required before posting as this is the public arena.
Anything to do with the trade or in and around it ...H&S pic's welcome.

Beware plumbers!!!.jpg

I've posted this a few times and this is at a mates house following a kitchen refirb several yrs ago. :omg_smile:

Beware plumbers!!!.jpg
 
To be fair, I would have been happy if it was a proper stainless steel Jubilee clip...the bzp skimpy ones are just rubbish!
You can also avoid corrosion by using a plastic cable tie...they won't harm the armouring at all!
Not sure you should be using stainless steel on SWA as the armour strands are galvanised. Looks like it should be the cable tie!
 
The 4 x 2.5 cables in the 32a mcb isn't that uncommon

A mate I know fits garage roller doors , if the consumer unit is in the garage he will wire a 2.5 straight into a 32a mcb

I have tried to explain to him this is a 'new circuit' be he literally don't give a sh!t and has done 100s of electric garage doors
 
The 4 x 2.5 cables in the 32a mcb isn't that uncommon

A mate I know fits garage roller doors , if the consumer unit is in the garage he will wire a 2.5 straight into a 32a mcb

I have tried to explain to him this is a 'new circuit' be he literally don't give a sh!t and has done 100s of electric garage doors
Now I’ve always been of the understanding that a single 2.5 radial circuit can’t be any more than 20a. Regardless of how many conductors you shoehorn in. 🤷🏼‍♂️

I was also told not more than 2 conductors in any MCB but often see 3 and 4. Especially with light and smoke detector combined circuits.

But that could have just been a ‘personal regulation’ from Guru Graham (my instructor).
 
The four 2.5mm2 radials are OK as long as there is a maximum of one 2G 13A socket on the end of each. I.e., a maximum load of 20A each.
If any of the radials feeds more than one socket, then a 13A FCU should be connected before the string of sockets, OR, as any sane person would do, the 32A MCB should be replaced by a 20 or 16A.
There is no limit to the number of wires to a MCB, as long as their total csa doesn't exceed the maximum for the terminal, and they are fitted in such a way that they are all secure.
I recently attended a "lighting MCB trips RCD" event, and found no less that 8 x 1.0mm2 connected to the MCB. Tracing the fault to just one light took minutes, without any floorboard lifting.
 
Last edited:
Mine was one that had 'grown' since the original install. The faulty circuit was one that I had actually added when I fitted a new central heating boiler. Boiler is in a W.C, accessed from outside, and I fitted an IP55 light switch inside the door, with a 20mm conduit up into the ceiling. A shower enclosure has since been fitted in the bathroom above, and it has a small leak, directly above the top of my conduit. Switch was half full of water.
What are the odds?
 

Reply to the thread, titled "Dodgy trade pictures for your amusement! - 1 Million Views!" which is posted in UK Electrical Forum on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Daily, weekly or monthly email

Back
Top