Got a call out to a cooker tripping the RCD every time the oven is switched on. But the time taken would vary. Suspected a failing element.

So went and had a look, tested the element. It registered 25.9ohms so about right for the size of the oven.

Checked all the wiring and took the bulb out to check that as seen issues with those before.

Noticed how the consumer unit was oddly set up but will get to that shortly.

So next tested the RCD.

Trip was fine at 38.6ms.
Ramp test was 19mA which is a little sensitive but above the 15mA minimum.

So next I put my clamp meter on the connections in the back of the oven. It was leaking around 3-4mA until the temp is set. Once the temp is set the leakage then climbs to around 13-14ma and fluctuates between 5-14mA (before the RCD trips).

So looking at the board I can hazard a guess that because they have stuck all the high power circuits on one RCD and all the lights on the other. We have got a case of accumulative leakage tripping the RCD as when the other circuits are off and just the oven is on. The RCD stays on.

[ElectriciansForums.net] Dodgy trade pictures for your amusement! - 1 Million Views!


[ElectriciansForums.net] Dodgy trade pictures for your amusement! - 1 Million Views!


Whilst there I noticed the wiring for the outside light. But another electrician apparently said this is ok as it’s out of reach. 🤔

[ElectriciansForums.net] Dodgy trade pictures for your amusement! - 1 Million Views!
 
So next I put my clamp meter on the connections in the back of the oven. It was leaking around 3-4mA until the temp is set. Once the temp is set the leakage then climbs to around 13-14ma and fluctuates between 5-14mA (before the RCD trips).
I would check for reversed polarity at the oven, in case it is the neutral that is being switched off so higher leakage once cycling.

Whilst there I noticed the wiring for the outside light. But another electrician apparently said this is ok as it’s out of reach. 🤔
Oh FFS!

That is a good advert for why T&E is not a suitable outside choice. Even if out of reach, which is a load of balls, then once it leaks you risk the lights on RCD going off mid winter.
 
Looking closely at that picture, I'd say that twin and earth was already in that condition when it was installed on that wall.
Apparently it’s been up there a few years. I don’t think it was like that when it was installed. I’m going back in a couple of days to sort it so will take a closer look when I remove it.
 
Apparently it’s been up there a few years. I don’t think it was like that when it was installed. I’m going back in a couple of days to sort it so will take a closer look when I remove it.
It's been moved since it decayed, I'd bet money. Has the wall been repointed recently? Might explain things.
 
It's been moved since it decayed, I'd bet money. Has the wall been repointed recently? Might explain things.

Pass, I'll ask when I go back. I did notice the clips looked quite new. Maybe the electrician who said it was ok as it's out of reach put some new clips in for them. You know just to keep it out of reach and compliant.....
 
Got a call out to a cooker tripping the RCD every time the oven is switched on. But the time taken would vary. Suspected a failing element.

So went and had a look, tested the element. It registered 25.9ohms so about right for the size of the oven.

Checked all the wiring and took the bulb out to check that as seen issues with those before.

Noticed how the consumer unit was oddly set up but will get to that shortly.

So next tested the RCD.

Trip was fine at 38.6ms.
Ramp test was 19mA which is a little sensitive but above the 15mA minimum.

So next I put my clamp meter on the connections in the back of the oven. It was leaking around 3-4mA until the temp is set. Once the temp is set the leakage then climbs to around 13-14ma and fluctuates between 5-14mA (before the RCD trips).

So looking at the board I can hazard a guess that because they have stuck all the high power circuits on one RCD and all the lights on the other. We have got a case of accumulative leakage tripping the RCD as when the other circuits are off and just the oven is on. The RCD stays on.

View attachment 104526

View attachment 104525

Whilst there I noticed the wiring for the outside light. But another electrician apparently said this is ok as it’s out of reach. 🤔
Peeves me when they go to the expense of fitting a spd, but then skimp on a split load board.
 
I would also be looking at that oven again as that leakage is way too high, Should be around 1 mA or 1 mA/kW of rated power

RCD with a rated operating current of 30 mA, the maximum leakage current is 9 mA
 

Reply to Dodgy trade pictures for your amusement! - 1 Million Views! in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Merry Xmas to all :D
    • Friendly
    • Like
Replies
8
Views
397
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
737
  • Sticky
  • Article
Thanks so much for sharing this with us! I’ll definitely take a look, it seems like there are a lot of useful and interesting products. The idea...
    • Like
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top