M

martinsayer81

hi guys, new to this, this is my first post.

a 3 bed, 2 bathroom house with a T-N-S 60Amp main cutout fuse, has a 6 way c/u with re-wireable fuses. (no spare ways)
3x 5A lighting circuits
2x 30A ring mains
1x 15A immersion heater
(oven and hob is gas)

the house is being extended and refurbished, and the architect has requested a new lighting circuit and a new kitchen ring main.

after looking at diversity, am i right in thinking that the demand will be too high for the 60Amp main cut out fuse??

will it need replacing with a 100Amp fuse with new 25mm meter tails,

many thanks for any replies/answers.

i am worried about telling the customer they need to replace the supply(costing them money) if its not necessary
 
yeah im changing the cu to a new split load board, adding new light circuit and ring for kitchen, and im going to put smoke alarms on one of the lighting circuits, with smokes interlinked,

just hope the existing installation doesnt have an underlying fault that will trip the rcd!!!

Lookout for "Borrowed Neutral" on the existing lighting circuits.
 
Martinsayer81

look at the current / time graph for that 60A fuse.

You'll soon realise something major will be required to happen to make it blow.

It'll run at 100A for a long time. A long time.

PS only main fuse I have ever heard of that had blown in a house (that I can think of) was because .... well a sparky did something very very silly!
 
well, some years agoe. around 1988, i blew the DNO fuse after moving into my dad's house to look after him. then again it was a 30A rewireable, been there since 1926.
 

Reply to does 60Amp main cut out need increasing?? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
279
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
776
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
787

Similar threads

Joining the ends of the radials together to form a ring, and changing the circuit protection to a single 32A would solve the MCB overload problem...
Replies
8
Views
732
Haha yes, it is. Must be a northern expression. Have a Google 😂
Replies
3
Views
315

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top