Does a cable have to have a CPC? | on ElectriciansForums

Discuss Does a cable have to have a CPC? in the UK Electrical Forum area at ElectriciansForums.net

Gringoking88

-
DIY
Joined
Jun 18, 2015
Messages
176
Reaction score
58
Location
London
Hi all,

Hope you are all well and all is good.

I'm having to install an EV charger tomorrow on a 3 phase TN C S earthing system, however, I need to TT just the charger and am going to put in a spike and run the earth only to charger keeping separate from the main supply fuse board. My question is, can I use a 4 core hi tuff cable from the main board to the charger and not have a cpc in it as it won't be used for the earthing anyway the supply will be RCD via type A rcbos, or do I have to use a 5 core cable with a CPC?

Thanks in advance and appologies if this is obvious and I'm just missing it.

M
 
Hi.
The regulations state that every point in a circuit needs to have a CPC that is connected to the main earth at the origin. In this case, to the earth rod. The CPC does not have to be contained within the cable itself necessarily, and if a separate CPC is to be run, it either has to be mechanically protected, or have a minimum csa of 4mm².
Obviously it's a bit last minute now, but you would probably be better using a 5 core cable.
 
i guess all depends if it’s cheaper to run a smaller supply cable with seperate earth cable or a bigger cable with the requisite number of cores
 
I would say the cable itself needs it. A cpc is a circuit protective conductor and the cable is part of the circuit.

what if they get a different charger in the future and at that time it needs a cpc
 
Hi all,

Hope you are all well and all is good.

I'm having to install an EV charger tomorrow on a 3 phase TN C S earthing system, however, I need to TT just the charger and am going to put in a spike and run the earth only to charger keeping separate from the main supply fuse board. My question is, can I use a 4 core hi tuff cable from the main board to the charger and not have a cpc in it as it won't be used for the earthing anyway the supply will be RCD via type A rcbos, or do I have to use a 5 core cable with a CPC?

Thanks in advance and appologies if this is obvious and I'm just missing it.

M
TT'ing the charger whilst required for a.lot of chargers can be the most obvious option.Pen fault detection units are they way to go. Good chargers have it built in.
For sake of an extra core in the cable run a cpc from the origin. On a 20m run it will add less.than ÂŁ20 to cost and alleviate the issue.
I note you are using hituff - swa could be better as you have the armour to use as a cpc... Swa is often cheaper too as its more commonly stocked.
With EV installs ot amazes me how many people try to do the bare minimum to install it. Spend just a little bit more time and money and the install is so much better.
 
Hi.
The regulations state that every point in a circuit needs to have a CPC that is connected to the main earth at the origin. In this case, to the earth rod. The CPC does not have to be contained within the cable itself necessarily, and if a separate CPC is to be run, it either has to be mechanically protected, or have a minimum csa of 4mm².
Obviously it's a bit last minute now, but you would probably be better using a 5 core cable.
Hi,

Thanks for the advice appreciated, think I will run it in 5 core swa and run the earth back to the board keeping it separate from the pme earthing system.
 
TT'ing the charger whilst required for a.lot of chargers can be the most obvious option.Pen fault detection units are they way to go. Good chargers have it built in.
For sake of an extra core in the cable run a cpc from the origin. On a 20m run it will add less.than ÂŁ20 to cost and alleviate the issue.
I note you are using hituff - swa could be better as you have the armour to use as a cpc... Swa is often cheaper too as its more commonly stocked.
With EV installs ot amazes me how many people try to do the bare minimum to install it. Spend just a little bit more time and money and the install is so much better.
Hi,

Normally we use Garo units as PEN fault detection units, however, this is a 3 phase installation so a rod is much cheaper in this scenario. Agree with the cost difference in cable, I will go with 5 core SWA. It wasnt so much the money, it was more about the efficancy of the installation not to mention the client does not want a massive 3 phase PEN fault detection unit.

Appreicate the advise,
 
Hi,

Thanks for the advice appreciated, think I will run it in 5 core swa and run the earth back to the board keeping it separate from the pme earthing system.
if you are using SWA you can use 4 core, armout as cpc for the SWA but isolated from the TT charger installation.
 

Reply to Does a cable have to have a CPC? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
312
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
834
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
941

Similar threads

This was posted this week, on topic ....... https://niceic.com/newsletter/omission-of-overload-protection/?dm_i=7G1W,7GCE,K4L2A,WHET,1
Replies
8
Views
710
  • Question
That was my saying not long ago about TNS to PME system. I would be nice you can ring up the DNO, will the systems being up graded, there is a...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top