To my understanding it would be ideal to test and inspect before energisation, but it isn't 100% necessary. If it leaves a client without power, it breaches health and safety (no power to safety services etc) or inconveniences them I'd have thought it would be reasonably practicable to turn on the juice and test ASAP.
 
To my understanding it would be ideal to test and inspect before energisation, but it isn't 100% necessary. If it leaves a client without power, it breaches health and safety (no power to safety services etc) or inconveniences them I'd have thought it would be reasonably practicable to turn on the juice and test ASAP.
You couldn't really have any confidence in that circuit/s unless you do.

In the case of a Cu change, for instance, why would you not test before energising ?
The power is only going to be going off again when it comes to testing, which will end up having no power for a longer time overall, unless you don't bother testing at all.
 
To my understanding it would be ideal to test and inspect before energisation, but it isn't 100% necessary. If it leaves a client without power, it breaches health and safety (no power to safety services etc) or inconveniences them I'd have thought it would be reasonably practicable to turn on the juice and test ASAP.

You're not really going to energise the system without doing the testing though are you. Surely the customer has been told that the power will be off during the CU change??

Yes, the testing is necessary.

In any case, you'd have to switch the power back off to do the dead tests, so what's the advantage of rushing to get the power back on before this?
 
Last edited:
How do you 'Change' a consumer unit without turning off the power ? Ok doing a little bit of dead testing might and an extra 25mins to the power being off but thats about it on an average board change. You could just switch everything on (the Bang Test) and hope for the best, but that is not the right way Imo
 
Ok,

To explain the situation... it's 4am, The electrician has been working since 8am. Beginning the testing process will be dangerous as the electrician is too tired to continue. The CU is installed properly so won't go bang an inspection of the CU shows this. If it is not energised there are severe disruptions... ambulance access, police access, security patrols are disrupted etc and the fire alarms & emergency lighting are affected to the premises.

Like I said, ideally, it would be tested but in this situation... but the regs just say reasonably practicable.
 
Ok,

To explain the situation... it's 4am, The electrician has been working since 8am. Beginning the testing process will be dangerous as the electrician is too tired to continue. The CU is installed properly so won't go bang an inspection of the CU shows this. If it is not energised there are severe disruptions... ambulance access, police access, security patrols are disrupted etc and the fire alarms & emergency lighting are affected to the premises.

Like I said, ideally, it would be tested but in this situation... but the regs just say reasonably practicable.
I should have been tested before the Cu was fitted ?
 
Ok,

To explain the situation... it's 4am, The electrician has been working since 8am. Beginning the testing process will be dangerous as the electrician is too tired to continue. The CU is installed properly so won't go bang an inspection of the CU shows this. If it is not energised there are severe disruptions... ambulance access, police access, security patrols are disrupted etc and the fire alarms & emergency lighting are affected to the premises.

Like I said, ideally, it would be tested but in this situation... but the regs just say reasonably practicable.

That's quite a specific example!

For such a critical installation then the job has been badly planned. And the bang test is certainly not appropriate.
 
Ok,

To explain the situation... it's 4am, The electrician has been working since 8am. Beginning the testing process will be dangerous as the electrician is too tired to continue. The CU is installed properly so won't go bang an inspection of the CU shows this. If it is not energised there are severe disruptions... ambulance access, police access, security patrols are disrupted etc and the fire alarms & emergency lighting are affected to the premises.

Like I said, ideally, it would be tested but in this situation... but the regs just say reasonably practicable.
Where is this DB.
 
That was my thinking, system had periodic inspections and the initial verification.

Job was planned by the bosses, timing and planning not up to the electrician.

Advice to next shift on at 8am to test critical systems given. Client happy to wait a further 4 hours. They neither tested nor re-energised. Left no power for 2 days.

When it was tested... and re-energised... no bang.

Has caused a bit of a thing at work. Just wondering which way to go.
 
That was my thinking, system had periodic inspections and the initial verification...

...Has caused a bit of a thing at work. Just wondering which way to go.

The reason given for not doing anything was there was a C3 fault. The board installed was smaller than the original so conduit no longer fitted. (Not installers choice) it was planned to be boxed in. This was predicted and reported to management. Knockouts were given grommet strip edging.

Tbh... I'd have tested it, powered it up and said get the joiner in ASAP. (I think the 2nd shift are just bullying the original electrician)
 
The C3 where conduits no longer line up with knockout holes…. Is there a gap now with basic insulation showing between the conduit and the DB?

Could have been solved with a bit of trunking?
 
Last edited:
The C3 where conduits no longer line up with knockout holes…. Is there a gap now with basic insulation showing between the conduit and the DB?

Could have been solved with a bit of trunking?
Yes we used to run some galv trunking horizontal butted up to the board and take the conduits into the trunking which means no gaps or mis-aligned old conduits in the new DB
 

Reply to Does a CU swap require a full initial verification on all circuits before it can be energised? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
433
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top