Had an interesting one this week, customer assures me he's on TT, DNO days the same but i'm getting 0.13Ohms on the Ze, never seen it that low befor.

There's no 100mA RCD on the supply and it doesn't look as if there's ever been one, so with that reading i'd assumed it was a TN system... so my question is do i now need to put on it as its TT? I'm assuming i do but with a reading that low is it still required?

My Regs book is in the van elsewhere... Thanks.
 
ok sorry! my bad, hope everyone enjoyed a chuckle at my expense!

Clearly the lower the better but I just had 21 ohms in my head from somewhere. anyone care to explain the significance of this figure I would greatly appreciate it!!!
 
Thanks Richard, i must have been on another planet when I posted my first comment!
Although Engineer54 claims my max 200 ohms comment is nonsense. Is this true? BS7671 states 200 ohms does it not? although I believe the NICEIC like to specify 100 ohms max.
Perhaps Engineer54 has been brainwashed by Tony Cable and his band of merry 'reg making' men.
 
Ive heard of people sprinkling copper filings in the soil around earth rod to improve reading, was this common practice at any time or just a 'trick of the trade' ???

Nope it's not any trick of the trade that i've ever seen or heard about. Powered carbon in a mortar mix i know of , but never heard of copper fillings. Can't see as that will make any difference myself, copper isn't exactly moisture retaining is it!! lol!!
 

Reply to Does a TT Earth 0.13Ohms require a 100mA incomer? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
559
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
993
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
926

Similar threads

  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
792
  • Question
Yes Table 3A that was in Appendix 3 of the 17th edition of BS7671 and in BS 7671:2018 (Blue Book) up to the release of BS7671:2018 +A2:2022 (Brown...
Replies
11
Views
951

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top