Does anybody know of this new regulation that omits the ZS test.

Discuss Does anybody know of this new regulation that omits the ZS test. in the UK Electrical Forum area at ElectriciansForums.net

sham

-
Reaction score
72
On another forum about an high ZS reading about a fused spur feeding a boiler, someone replied that in the new 18th regs if the RCD breaks the circuit within time under test you do not need to check ZS, just R2 continuity test for CPC continuity would be good enough. You just put N/A on the test form for Zs. He even posted an article from Stroma.
This was a response to a question about the Zs reading with his Instrument was 100 ohms higher than his calculation.
Does anybody know more about this, and is it because of rcds and rcbos causing high reading on live ZS redings ?

42806519_1911455935588038_6381880673786920960_n.jpg
 
MCBS are for short circuits. There has been cases of Live and Neutral touching and it just trips the MCB and not the RCD. It seems that the regs are saying we can't rely on the zs being low enough to help trip the MCB in time which may cause the cable to be permanently damaged or appliance, but we still have protection of persons and livestock by the use of RCDs. This is my thoughts at the moment.
 
MCBS are for short circuits. There has been cases of Live and Neutral touching and it just trips the MCB and not the RCD. It seems that the regs are saying we can't rely on the zs being low enough on an TT system to help trip the MCB in time which may cause the cable to be permanently damaged or appliance, but we still have protection of persons and livestock by the use of RCDs. This is my thoughts at the moment.
 
I
Well yes, RCDs don’t work on L - N faults
I'm saying that the Regs when it comes to TTs, it that we can't always garantee the disconnection of the mcb circuit on time and that it may damage property but as soon it leaks to livestock or people , it must trip within the time and the continuity of CPC must be sound. And results must be recorded.
 
This thread hasn't been replied to for 14 days, so replying to this one may not get a response. Post a new thread instead.

Reply to Does anybody know of this new regulation that omits the ZS test. in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock