On another forum about an high ZS reading about a fused spur feeding a boiler, someone replied that in the new 18th regs if the RCD breaks the circuit within time under test you do not need to check ZS, just R2 continuity test for CPC continuity would be good enough. You just put N/A on the test form for Zs. He even posted an article from Stroma.
This was a response to a question about the Zs reading with his Instrument was 100 ohms higher than his calculation.
Does anybody know more about this, and is it because of rcds and rcbos causing high reading on live ZS redings ?

[ElectriciansForums.net] Does anybody know of this new regulation that omits the ZS test.
 
MCBS are for short circuits. There has been cases of Live and Neutral touching and it just trips the MCB and not the RCD. It seems that the regs are saying we can't rely on the zs being low enough to help trip the MCB in time which may cause the cable to be permanently damaged or appliance, but we still have protection of persons and livestock by the use of RCDs. This is my thoughts at the moment.
 
MCBS are for short circuits. There has been cases of Live and Neutral touching and it just trips the MCB and not the RCD. It seems that the regs are saying we can't rely on the zs being low enough on an TT system to help trip the MCB in time which may cause the cable to be permanently damaged or appliance, but we still have protection of persons and livestock by the use of RCDs. This is my thoughts at the moment.
 
I
Well yes, RCDs don’t work on L - N faults
I'm saying that the Regs when it comes to TTs, it that we can't always garantee the disconnection of the mcb circuit on time and that it may damage property but as soon it leaks to livestock or people , it must trip within the time and the continuity of CPC must be sound. And results must be recorded.
 

Reply to Does anybody know of this new regulation that omits the ZS test. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
412
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top