Or---- get a joiner to band a nail through a cable. that should bring it down
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss does anyone could help,high Zs value in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
well,I can not test Zs on high because rcd would trip obviously,but Ze why i should test on non trip if there is no Rcd protection?tnxif you were testing Ze on high and Zs on no trip, then I just thought that it was possible that this was the reason for the difference. Testing Ze on no trip would rule this out.
oh I see!no mate I thought the same ,that is only the one installation I can not understand .the procedures I'am keeping the same.I only suggested it to see if it was a fault on one of the settings on your testers
Right!Can you read? If so, read my posts again. What I am trying to say is that you need a common denominator to rule out a fault in the testers (not that this would totally rule this out), but if I were you I would try it.
Just read this thread and having had a think about the current path am wondering if the main switch might have a high resistance contact in it. Could explain the uniformly high direct Zs readings you're getting. If you've got a spare, try swapping the main isolator and retest. Also if you have an isolator fitted after the meter but before the CU this is also a possible fault location.
Just have a think about where those electrons are flowing and elliminate every switch and union one by one. You'll get it!
sorry mate just notice I have post a wrong message to You!I'd carry out a zs test at the main switch at the DB, then on the MCB's to see if the RCD's or MCB's are giving any additional impedance.
huh?
sorry mate just notice I have post a wrong message to You!
But thank You very much for an advise,I did the test as You sed and You are right the problem is with the rsd,s or with the main isolator,i will have to do just another test at the isolator on its own.But I got the answer,where is the problem,thank's a lot mate!!