Does this need to be bonded? | on ElectriciansForums

Discuss Does this need to be bonded? in the UK Electrical Forum area at ElectriciansForums.net

HappyHippyDad

-
Esteemed
Arms
Supporter
Joined
Dec 18, 2011
Messages
5,320
Reaction score
6,561
Location
Gloucestershire
I have just put in a sub distribution board in the middle of a field for a new supply for some poly tunnels (soil heating mats and lighting). I have made it a TT.

I have noticed that they have concreted in a number of separate metal hollow poles (see picture) which will be part of the polytunnel. I haven't tested these yet, but they will test as extraneous. If they remain as they are (i.e accessible) do they require Main bonding?

I do get confused with bonding! Every year I re-read up on it, feel I've got it, and then either forget it or a new scenario comes along!

My thoughts are that it will need a 10mm into the nearby DB as it is an 'exposed metallic structural part of the building', which is one of the examples of an extraneous conductive part (411.3.1.2). However, each post is a separate piece of extraneous, so I need to continue this 10mm around the poly tunnel to each post. Is this right? Or, does it not require bonding for whatever reason?

PS.. there will be no livestock in the field at any time.

[ElectriciansForums.net] Does this need to be bonded?
 
I can't see why you would. They are outside already so will be at true earth potential and by the look of the photo not a part of the electricsl installation so are just pieces of metal. I could be wrong but if they aren't exposed conductive parts and aren't part of a structure then, i dont see why they would need bonding. Otherwise we will be bonding every random piece of outdoor metal.
 
I get why you are asking. They pass the 3 point test for being extraneous conductive parts.
I know it sounds odd, but I think I'd loop test them!
I'd want to know whether there is any point/benefit connecting a metal pole in the ground to a metal rod in the ground, and whether it actually lowers the impedance to any degree that is meaningful.

I'm sure everything in there will be RCD protected and you'd need arms like Mr Tickle to touch two of them at once. If it proves that they have reasonable impedance anyway I currently don't see the point of bonding them.
 
In the event of a faulty rcd that doesn’t disconnect on a TT system in the event of a fault, I think I’d rather as few exposed conductive/extraneous metal parts as possible.

Will there be a floor going in the poly tunnels or will you effectively be standing in the dirt?
 
In the event of a faulty rcd that doesn’t disconnect on a TT system in the event of a fault, I think I’d rather as few exposed conductive/extraneous metal parts as possible.

Will there be a floor going in the poly tunnels or will you effectively be standing in the dirt?
I expect they'll be standing on the earth/dirt.
 
Assuming that they are extraneous and that they will be extended with metallic hoops to for the structure of the polytunnel, I would say that they need to be bonded. You've mentioned a lighting installation, so it might be possible to touch a light fitting and a hoop simultaneously? Also, what about the controls for the heating? Where will they be located and do they have exposed conductive parts?

You may not need a 10mm bonding conductor. Have a look in GN8 as you may be able to use 6mm on your TT system.
 
Assuming that they are extraneous and that they will be extended with metallic hoops to for the structure of the polytunnel, I would say that they need to be bonded. You've mentioned a lighting installation, so it might be possible to touch a light fitting and a hoop simultaneously? Also, what about the controls for the heating? Where will they be located and do they have exposed conductive parts?

You may not need a 10mm bonding conductor. Have a look in GN8 as you may be able to use 6mm on your TT system.
Defo if accessories are fixed to the structure it will need MBPC.
Maybe the structure will be linked somehow, & thus only one MBPC point
 
Defo if accessories are fixed to the structure it will need MBPC.
Maybe the structure will be linked somehow, & thus only one MBPC point

That's what I was thinking - maybe all the arched poles are joined together by a central pole at the top.
 
Are these hollow pipes for the metal arches for the tunnel.
I suspect they'll be the hooped plastic pipe type supports... so MDPE water pipe just stuffed into those hollow pipes. The PVC sheeting, when tight, will be part of the structure... until a good gale of wind rips it and it all ends up in the next county !
 
You may not need a 10mm bonding conductor.
A 10mm metal bond is not required in this case as the resistance of the extraneous parts in question will be much higher than the usual extraneous items we deal with such as water pipes and other metallic services. A 4mm bond will be more than adequate.
 
It would still be fun to loop test them, if only
to have a good laugh if they have lower impedance than the official earth electrode….

We do have to remember that bonding in this case is joining a metal thing in the ground to another metal thing in the ground.
 
In the event of a faulty rcd that doesn’t disconnect on a TT system in the event of a fault, I think I’d rather as few exposed conductive/extraneous metal parts as possible.
It might be worth using a 100mA delay incomer, while providing little in the way if direct contact shock protection that way a fault will clear even if a final circuit RCD has failed.
 

Reply to Does this need to be bonded? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
521
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

If you can see a piece of plastic entering from the ground then (as cliff said), it does not need main bonding. I think (not sure) this is reg...
Replies
3
Views
327
  • Question
Why would the RCD fail … yes it can happen but then it may not. Without it you have no protection on the TT System
Replies
36
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top