Does this need to be bonded? | Page 3 | on ElectriciansForums

Discuss Does this need to be bonded? in the UK Electrical Forum area at ElectriciansForums.net

HappyHippyDad

-
Esteemed
Arms
Supporter
Joined
Dec 18, 2011
Messages
5,349
Reaction score
6,604
Location
Gloucestershire
I have just put in a sub distribution board in the middle of a field for a new supply for some poly tunnels (soil heating mats and lighting). I have made it a TT.

I have noticed that they have concreted in a number of separate metal hollow poles (see picture) which will be part of the polytunnel. I haven't tested these yet, but they will test as extraneous. If they remain as they are (i.e accessible) do they require Main bonding?

I do get confused with bonding! Every year I re-read up on it, feel I've got it, and then either forget it or a new scenario comes along!

My thoughts are that it will need a 10mm into the nearby DB as it is an 'exposed metallic structural part of the building', which is one of the examples of an extraneous conductive part (411.3.1.2). However, each post is a separate piece of extraneous, so I need to continue this 10mm around the poly tunnel to each post. Is this right? Or, does it not require bonding for whatever reason?

PS.. there will be no livestock in the field at any time.

[ElectriciansForums.net] Does this need to be bonded?
 
You would get 7.67k ohms with the calculation given. It's just that the calculation we generally use includes taking off 1k ohms for resistance through the body. Hence 22k rather than 23k, or in this case 6.67k rather than 7.67k.
So which of the above figures would be regarded as the cut off point for when something is regarded as extraneous?. There is quite a gap between 7.67 and 22 Kohm.
 
So which of the above figures would be regarded as the cut off point for when something is regarded as extraneous?. There is quite a gap between 7.67 and 22 Kohm.
I'm about to sit down to a cup of earl grey and a few pieces of toblerone to watch a film, so i'm afraid I haven't got the regs to hand. However, this PDF explains it quite well.
I would always class anything below 23K ohms as extraneous.
 

Attachments

  • Extraneous-conductive-parts-17_edition_factsheet_05.pdf
    103.4 KB · Views: 43
Assuming that they are extraneous and that they will be extended with metallic hoops to for the structure of the polytunnel, I would say that they need to be bonded. You've mentioned a lighting installation, so it might be possible to touch a light fitting and a hoop simultaneously? Also, what about the controls for the heating? Where will they be located and do they have exposed conductive parts?

You may not need a 10mm bonding conductor. Have a look in GN8 as you may be able to use 6mm on your TT system.

Your ECA doc gives a clear explanation and I think I would want to bond it if the hoops are metallic (they may well be plastic). It's all about keeping simultaneously accessible bits of metal at the same potential (or no potential at all if they're not extraneous - ie don't bond random metal bits and bobs if they're not extraneous!). The fact it's TT makes no difference and if the RCD fails makes it all the more important.
 
Your ECA doc gives a clear explanation
Won't download for me. What's the doc called?. I can Google it
. It's all about keeping simultaneously accessible bits of metal at the same potential
If simultaneousely accessible and class 1 accessories are used then that changes the scenario significantly. But I understand that previous posts established that the metal posts were not simultaneousely accessible.
 
It's a great document and one of the clearest explanations I've ever seen.
I'm not sure it helps this situation though other than establishing a helpful target let-go current.
See the diagram below and note the bit circled. That wouldn't be there in the situation this thread is discussing.

Isn't the point here that in all cases there's an 1000 ohm path straight to earth with at least 230ma current flowing, whether you add a parallel path through a unbonded pole (roughly 1000+ 110 ohms using value to MET) or a parallel path through an bonded pole (roughly 1000 + 66 ohms)?
Am I thinking about this right or losing marbles?!
[ElectriciansForums.net] Does this need to be bonded?
 
It's a great document and one of the clearest explanations I've ever seen.
I'm not sure it helps this situation though other than establishing a helpful target let-go current.
See the diagram below and note the bit circled. That wouldn't be there in the situation this thread is discussing.

Isn't the point here that in all cases there's an 1000 ohm path straight to earth with at least 230ma current flowing, whether you add a parallel path through a unbonded pole (roughly 1000+ 110 ohms using value to MET) or a parallel path through an bonded pole (roughly 1000 + 66 ohms)?
Am I thinking about this right or losing marbles?!
View attachment 94766
No. Your marbles are very much where they are meant to be. But if I may offer my final comment on this post, it's this. Bonding as a topic is the "gift that keeps on giving" from the point of view that since I, ve been an apprentice no other single electrical subject has caused me more "head scratching" (along with the occasional headache.) The electrical game would be very boring without it🙂
 

Reply to Does this need to be bonded? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hope everyone has had a great Christmas and here’s hoping we all have a better new year coming our way ! Remember our riches aren’t measured by...
    • Friendly
    • Like
Replies
11
Views
544
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
758
  • Sticky
  • Article
Thanks so much for sharing this with us! I’ll definitely take a look, it seems like there are a lot of useful and interesting products. The idea...
    • Like
Replies
5
Views
2K

Similar threads

If you can see a piece of plastic entering from the ground then (as cliff said), it does not need main bonding. I think (not sure) this is reg...
Replies
3
Views
403
Hi I need help with understand supplementary bonding. I know RCD is additional protection and in the even of the fault at leakage of 30mA, it...
Replies
0
Views
76

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top