DOL starter switch Trips out | Page 2 | on ElectriciansForums

Discuss DOL starter switch Trips out in the Electrical Engineering Chat area at ElectriciansForums.net

I presume that you are measuring between a live pin and an earth or N when taking the measurements.

when measuring voltage across the contactor, measure like this.
p.s. it works better when the contactor is under load and use a volt meter instead of a pair of biro's

Yes Live and earth on contactor, will find some biro's and do it again
 
Definitely a fault on L1 I would check what James has listed It may well be an isolator or supply cable upstream feeding the DOL that is failing causing a high resistive joint looking at the current readings

Upstream from the DOL is another CeeForm connector plug, will check that. and there is then a choice of sockets as there are various other feeds going to various other Motors on the spud grader. Which were not powered at time of test by the way.
[automerge]1579189138[/automerge]
And compare it with the motor FLA on the nameplate and the current setting of the starter. Surely if the starter keeps tripping on overload, the first thing you would do is see if it is overloaded?
Hi Lucian

See pic of the overload, I'm reading it as 6.5A, what do you think?

Either way turning it up or down makes no difference to the problem, its now set at 5.5

Thanks for your input
 

Attachments

  • [ElectriciansForums.net] DOL starter switch Trips out
    20200116_124231.jpg
    64.1 KB · Views: 14
Last edited:
Good Luck! won't be back on till Monday i'll see how you get on then! just another thought is that its worth checking the voltages on the other equipment upstream from the contactor as the voltage would still be low on L1 further up stream
 
So, to recap:
Problem with conveyor motor tripping overload relay after a minute.
Nameplate FLC 5.1A
Starter overload was found set at 6.5A
Measured line currents 12.5 / 7.6 / 1.5A at 218 / 240 / 230V L-N after O/L
Winding resistances L-star point all 2.99 ohms

The disparity between the line currents is much greater than that of the voltages at the starter, so I think the different voltages are more a symptom of different drop in the circuit conductors carrying different currents, and less likely to be the cause. As yet we don't have confirmation of the voltages at the motor terminals themselves so there is a possibility of a high-resistance connection between the two.

Another possibility is that the motor has a faulty winding with a few shorted turns that is too small a fraction of the winding resistance to register on the resistance test. Nonetheless, when energised with AC, the transformer action with the shorted turns causes all sorts of problems within the motor, not least lots of heat, although it doesn't run for long enough for that to become apparent.

One simple but effective test is to change the leads around in the motor terminal box to put each winding on a different supply phase. I.e. move L1 to L2, L2 to L3 and L3 to L1 to preserve the sequence. Then re-measure the line currents. If the cable with the 12.5A overcurrent is now L2, the problem is in the motor. If it's still L1, the problem is with the wiring or starter.
 
[ElectriciansForums.net] DOL starter switch Trips out
above is a stock picture of roughly what you have.
Imagine that the contact between 4 and C has burned away
with the contactor energised.
If it has completely gone and there is no connection at all then you will get the following slightly misleading readings (approximate)
N to L1 230v
N to L2 230v
N to L3 230v

N to 2,3,4 all 230v assuming the fuse's have not failed

N to A 230v
N to B 230v
now here's where it can get a bit confusing
N to C will be less than 230v but not a lot less. It will not be Zero volts as you might expect.
this is because the voltages from L1 and L2 pass through the motor windings and return to point C to be measured by your meter in reference to N

the following readings are what i would expect in the picture above
2 to A 0v
3 to B 0v
4 to C 400v

now in the real world, the contacts will probably not have burned away so there is absolutely no connection, just a very high resistance so the figures above are all approximate. but you get the idea? this type of fault finding is a quick and easy way to determine where you are dropping voltage on one phase that is causing overcurrent on the other phases.
You can use the same technique on the overload, any fuses or isolator in line etc.
 
Your point about the regeneration of a mssing phase is good and valid and this is a trap for the unwary. However, one thing pointing away from the intermittent / burnt-out contact scenario is that the OP has not mentioned any issues with starting. The motor appears to start from a standstill every time, which a 3-phase motor won't generally do if one line is missing entirely. My experience is that it is more likely on a star-delta starter where it starts OK in star, then loses a phase when it transitions to delta but carries on running as a single-phase motor.
 
To have a true sense of the 3 phase voltages please measure L1-L2, L1-L3 and L2-L3 ie the line voltages instead of the phase voltages with respect to E. Depending on the earthing system the E you touch with your meter could be at some arbitrary potential with respect to the supply N.

Do some L-L (line) and L-N(phase) voltage measurements at the incomer and also the distribution board feeding the supply to the conveyor motor.

Study the distribution switchgear to discover if there are any large unbalanced single phase loads and on which phase they are connected.
 
Last edited:
So, to recap:
Problem with conveyor motor tripping overload relay after a minute.
Nameplate FLC 5.1A
Starter overload was found set at 6.5A
Measured line currents 12.5 / 7.6 / 1.5A at 218 / 240 / 230V L-N after O/L
Winding resistances L-star point all 2.99 ohms

The disparity between the line currents is much greater than that of the voltages at the starter, so I think the different voltages are more a symptom of different drop in the circuit conductors carrying different currents, and less likely to be the cause. As yet we don't have confirmation of the voltages at the motor terminals themselves so there is a possibility of a high-resistance connection between the two.

Another possibility is that the motor has a faulty winding with a few shorted turns that is too small a fraction of the winding resistance to register on the resistance test. Nonetheless, when energised with AC, the transformer action with the shorted turns causes all sorts of problems within the motor, not least lots of heat, although it doesn't run for long enough for that to become apparent.

One simple but effective test is to change the leads around in the motor terminal box to put each winding on a different supply phase. I.e. move L1 to L2, L2 to L3 and L3 to L1 to preserve the sequence. Then re-measure the line currents. If the cable with the 12.5A overcurrent is now L2, the problem is in the motor. If it's still L1, the problem is with the wiring or starter.

Hi Lucian,

Did as you suggested, but at the out going at the switch not at the motor, and yes the higher current moves to the next phase so I'm going with the motor being at fault.

Thanks for your input

Pip
[automerge]1579598814[/automerge]
To have a true sense of the 3 phase voltages please measure L1-L2, L1-L3 and L2-L3 ie the line voltages instead of the phase voltages with respect to E. Depending on the earthing system the E you touch with your meter could be at some arbitrary potential with respect to the supply N.

Do some L-L (line) and L-N(phase) voltage measurements at the incomer and also the distribution board feeding the supply to the conveyor motor.

Study the distribution switchgear to discover if there are any large unbalanced single phase loads and on which phase they are connected.
Hi,

There is no Neutral at the switch or motor.

Pip
 
Pip; May I express some minor frustration with you? A number of folk have asked if you measured the Insulation Resistance of the motor windings - have you? I asked you to measure the line voltages which you don't need an N or E to do - did you?

That said - well done Sir for finding a defective motor. :)
 
Hi Lucian,

Did as you suggested, but at the out going at the switch not at the motor, and yes the higher current moves to the next phase so I'm going with the motor being at fault.

Thanks for your input

Pip
[automerge]1579598814[/automerge]

Hi,

There is no Neutral at the switch or motor.

Pip
Marconi said Measure L-N voltage at the incomer Pip
 
Some very good advice on here. I often swop the phases round twice at the DOL so that I can see if a fault is incoming or on a motor.

One thing I want to add is removing the motor connection bars completely and checking the bolts underneath are tight, I´ve found them loose on old and brand new motors!
Be wary on old motors as the plastic terminal holder can become brittle and snap!
 

Reply to DOL starter switch Trips out in the Electrical Engineering Chat area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
953
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Hi James, At the inverter end the multi strand is ferruled and torqued in the terminal and at the motor end they are the “wago type” push fitting...
Replies
2
Views
381
Thanks all for the suggestions! Customer doesn't store anything else in the cupboard with the tank, not even towels or sheets. Heatrae stat is...
Replies
11
Views
1K

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top