lewlec,
Almost certainly due to high earth leakage by design of the drives rather than by any faults though.
yes.... agreed.
lewlec,
Almost certainly due to high earth leakage by design of the drives rather than by any faults though.
No - the frequency has to remain constant for this application. Didn't try taking it out either.
As discussed previously in this section, I think the VFDs might be on the small side - this is not helping the situation either. Will try the 300mA RCD and see how it goes.....
No, not the output frequency... I said the switching frequency.
By taking out the inverter you can find if the RCD still trips, which can point to another issue, perhaps.
Is the inverter good?
Has this machine ran at all since you've had it?
.
Take a look at page 86, parameter P297... switching frequency. Decrease it. I have seen in IMO manuals that switching freq. contributes to RCD tripping.