Hi all :).

Seeing alot of cases where I have seen 20A DP switches in a kitchen (for example) each feeding a radial 2.5t&e to each white goods appilance or similar, and the 20A DP switch primarys are fed from the 32A kitchen ring final circuits - Is this accepteble to BS7671?

I'm guessing if it's only serving a 1 gang s/o or 13A fused spur it would not be at risk of overload at the switch?

Please advise.

Many Regards

Jamie
 
They are switching spurs, not radials.
Technically it is acceptable under bs7671
My personal opinion based on what I was taught as an apprentice is that it is wrong. But thankfully we cannot judge an installation based on personal opinion
 
If it is supplying a 13 amp socket the yes it fine the 20 amp switch it just for remote switching but if the 20amp switch goes to a flex outlet then no as there is no overcurrent protection for the cable suppling the apliance
 
Like the others have said if each spur is just feeding one appliance then this is deemed OK with BS7671 (See Appendix 15, BS7671). Although it doesn't actually show a DP switch it shows a FCU suppplying the fixed equipment so possible this isn't in line with BS7671 as there is no fusing down for the flex to the appliance as with all other scenarios shown in Appendix 15?
 
Like the others have said if each spur is just feeding one appliance then this is deemed OK with BS7671 (See Appendix 15, BS7671). Although it doesn't actually show a DP switch it shows a FCU suppplying the fixed equipment so possible this isn't in line with BS7671 as there is no fusing down for the flex to the appliance as with all other scenarios shown in Appendix 15?

The fuse will be in the plug top for the appliance.
 
The fuse will be in the plug top for the appliance.

That would be the usual scenario Lee, but the OP just states DP switch going to appliance so I thought he meant straight to the appliance with no socket! He probably didn't mean that, as rereading that would not comply with BS7671, but it would be good to know if it was that?
 
Personally I'd rather use a switched/fused spur and run the feed to it as a spur from a nearby socket on the local RFC, connecting 3x 2.5 T&Es neatly in a single 25mm metal box can be a pain.
 
Hi all :).

Seeing alot of cases where I have seen 20A DP switches in a kitchen (for example) each feeding a radial 2.5t&e to each white goods appilance or similar, and the 20A DP switch primarys are fed from the 32A kitchen ring final circuits - Is this accepteble to BS7671?

Kitchen white goods such as washing machines, dish washers, under sink water heaters etc. Have a read of 554.3 - 554.3.3

It's also the way the manufacturers are asking for the neutral to be switched off locally for service and repair to safe gaurd against Neutral shocks.
 
I often use 20A DP switches for oven ccts these days, with any fusing down as necessary. I give the option of a 'proper' 32A cooker cct but many customers are happy with less. A lot of ovens don't pull much nowadays.
 
Last edited:
A 4 gang grid style bank of 20a dp switches is a far neater and modern way of isolating appliances. Use a shaver box for ease of connection. Appliances can be fused down via a plug or a un-sw fused outlet.
 
I wonder if the OP was questioning whether connecting the RFC conductors together in the feed side of a 20 amp rated switch could in itself cause an issue as on occasions there could be 30 amps + on those terminals ?
 
I wonder if the OP was questioning whether connecting the RFC conductors together in the feed side of a 20 amp rated switch could in itself cause an issue as on occasions there could be 30 amps + on those terminals ?

Someone please correct me if I am wrong:-

The 20A rating of a FCU is for the contacts within the switch and not the incoming terminals?
 
I agree the terminal should be able to take load as they are the same size as sockets and spurs and anyway the terminal will never run at 32amps as the ring circuit is distributed in 2 directions
 

Reply to Domestic: 20A DP switches and ring final circuits?? in the Domestic Electrician Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
252
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
724
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
703

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K
  • Question
I have to agree with Baldelectrician on almost everything he says except one ! I wouldn’t be walking away I’d be running lol. Definitely if your...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top