“Domestic” Cable for Motor Applications | on ElectriciansForums
Discuss “Domestic” Cable for Motor Applications in the Domestic Electrician Forum area at ElectriciansForums.net
IAmSparkytus!
Newcastle Upon Tyne
Good afternoon all,
First time posting on here so not sure if this is the correct place to post this but I’m sure you will all correct me if it isn’t.
My query today is whether anyone can see a problem using twin and earth to supply motor units fed from C rated MCBs?
I have enquired with an NICEIC assessor who says he doesn’t see the problem with it but still remain unsure and uncertain within my head.
Maybe this is unacceptable in all circumstances, maybe it’s ok for shorter runs but not larger runs, could be that it’s perfectly fine.
Please let me know your thoughts! Thanks.
All depends on the installation method and external influences.
Also how is the motor connected?
Is the cable and termination subject to vibration etc?
Need more info really.
When I used to wire motors up in the past it was a connection to a 4x4 box then either a copper or flex from the box to the motor as mentioned above its the vibrations as some motors sit on heavy duty rubber shock absorbers more info needed as then better advice can be given.
Good afternoon all,
Will that be single phase motors or three phase motors, solid core condctorsare not ideal for machines that are subject to vibration
In this instance there are 10 motor units positioned throughout a service duct which runs around the perimeter of a building.
The cables are grouped and tie wrapped to a cable tray, go into individual rotary isolators, and then into the units.
Cable runs range from 10-90 metres from the distribution board.
Is this already installed or are you installing? Is this perimeter run internal or external to the building?
This is an existing installation I have come across. The service corridor is internal with no chance of the weather affecting it.
Usual procedure for myself would be to install using SWA or NYY.
Reply to “Domestic” Cable for Motor Applications in the Domestic Electrician Forum area at ElectriciansForums.net
By retired electrician, I mean that I have retained my ticket but no longer do installation work. Thanks for the clarification. I missed that it...
I would agree that the motor is by far the best part to replace. if it is powered and not turning then it is broken. Keep it simple!