“Domestic” Cable for Motor Applications
Good afternoon all,
First time posting on here so not sure if this is the correct place to post this but I’m sure you will all correct me if it isn’t.
My query today is whether anyone can see a problem using twin and earth to supply motor units fed from C rated MCBs?
I have enquired with an NICEIC assessor who says he doesn’t see the problem with it but still remain unsure and uncertain within my head.
Maybe this is unacceptable in all circumstances, maybe it’s ok for shorter runs but not larger runs, could be that it’s perfectly fine.
Please let me know your thoughts! Thanks.
Disconnection times referring to the undersized CPC in T +E.
Vibration issues in terminations of the final length Rotary to Motor control are the answers picked up from the responses so far.
A J - disconnect times
Marvo - undersized CPC
Everyone else - vibration issue
With regards to Vibration issues, I was one of those who supported that, but what about MICC that had solid core conductors, although Electricians sometimeput a loop in the cable to counter act vibration.
No problem with disconnection times and the earths all seem suitably sized. 6mm twin and earth is the largest in place. There has been 2 x 10mm SY cables installed as well where the earth is obviously the same size as the line conductor.
Regarding the vibration issue, unless I’m missing something or not thinking fully, what difference would a stranded core cable make to a solid core cable if both had a nice tight connection? Or is it not the cable coming loose which you are getting at?
Thanks.
The name flexible cable will be the clue here, seeing as the motors will be vibrating a solid core cable is more liable to snap in the termination than a flexible one.
Excuse me if I’m being ignorant but what makes you think a solid core cable will snap with a bit of vibration unless the copper had been nicked or damaged?
Something that is of solid construction, is more prone to breakages than something that is flexible, especially solid conductors.
So Rotary isolator directly feeds and operates the motor, or is it some kind of unit with a motor incorperated ?
What size are the motors ?
Are they above 0.37kw ?
Any overload protection provided for the motors ?
Good afternoon all,
Using Twin and cpcfor this type of installation, is not the best Idea in the World.
Using Twin and cpcwill give you a reduced cpc size, then you will have the added problem with solid conductors which people have already commented on, what sort of cable entry are you intending to use, when terminating the twin and cpc? what does your experience and qualifications tell you about using this cable and this installation method? in my opinion asking the NICEIC help desk is like phoning up the Gas board to ask about a water leak, ie a waste of time. Apart from that it wont look very professional, imo.
What’s your opinion on the situation @ToonSparky?
As I have said above, I personally use SWA in this sort of installation.
I’m merely asking out of curiosity to see if there was anyone on this forum who would agree that it is fine to carry out the works in this way.
Agreed that I have asked the NICEIC about things in the past and they have come back with “we can’t advise you on that” to which I thought how can you be an assessor yet not give advice. Strange.
In this case however, the NIC bloke said it was fine to do which made me wonder other peoples thoughts on it.
Thanks.
IAmSparkytus!,
suffolkspark,