Hi Guys,

Take a look at the picture below. (you may have to turn your head as i couldn't work out how to rotate it it).
As you can see, the DB has seen better days so i am going to replace it with a nice new one with plenty of ways.

I don't get to involved with domestic work as i really only work with industrial installations and bigger stuff. Few questions you guys hopefully will be able to help me with. I will just add that this is a TT System to this house.

1) How far does does the main intake and DB need to be away from the Gas Meter?(As you can see, it is pretty close)

2) I done a Ze on the existing board and was getting a silly reading! Do i need to be looking at installing a new earth rod? If so where is the best place to put it?

3) Choosing a new DB. I was thinking of getting the usual 2 x RCD split boards. Now do i need an RCD Main Switch to feed the Split board (if that makes sense). and if i do does that main switch ideally need to be 100ma?

or

4) can i put a normal DB in with a 100ma main switch and RCBO's to feed each circuit.

I've been a spark for 14years but only ever work on industrial installations and dont know that much about the domestic side of things these days. There are just a few little question im just not sure about when it comes to some of the regs that are involved in domestic installations.

Cheers Guys


Steve



photo.jpg
 
First off install a new TT system, the existing one is a dead duck!! lol!! You need a minimum of 2 X 5/8'' extendable rods coupled together to give you the depth required to make the system a stable one, and with an added bonus of substantially lowering your Ra value. Locate the rod position at least 1m away (more is better) from any external house walls to miss original builders rubble etc. Oh, and use a flush to ground earth pit over the rod to protect the connection, and to facilitate future testing, as well as a visual means of identification of earthing location!!

Secondly, i wouldn't take any notice at all of richy3333 suggestion of NOT incorporating an S type 100 mA upfront RCD (which could be used in place of CU main isolator). This is a TT system, and totally relying on a single RCD for earth fault protection is not very sensible, The upfront S type RCD will be if you like, the Additional protection, that a normal RCD gives to a TN installation!! As for the type of CU you install that's up to you dual RCD, or the far better but costlier all RCBO...
 
First off install a new TT system, the existing one is a dead duck!! lol!! You need a minimum of 2 X 5/8'' extendable rods coupled together to give you the depth required to make the system a stable one, and with an added bonus of substantially lowering your Ra value. Locate the rod position at least 1m away (more is better) from any external house walls to miss original builders rubble etc. Oh, and use a flush to ground earth pit over the rod to protect the connection, and to facilitate future testing, as well as a visual means of identification of earthing location!!

Secondly, i wouldn't take any notice at all of richy3333 suggestion of NOT incorporating an S type 100 mA upfront RCD (which could be used in place of CU main isolator). This is a TT system, and totally relying on a single RCD for earth fault protection is not very sensible, The upfront S type RCD will be if you like, the Additional protection, that a normal RCD gives to a TN installation!! As for the type of CU you install that's up to you dual RCD, or the far better but costlier all RCBO...
I don't necessarily disagree about the 100mA RCD, but perhaps you could quote the REg that requires it? Just re-read my previous post I didn't say to NOT incorporate a time delayed 100mA RCD, but highlighted it is NOT a requirement of BS7671, unless of course you can advise differently?
 
I don't necessarily disagree about the 100mA RCD, but perhaps you could quote the REg that requires it? Just re-read my previous post I didn't say to NOT incorporate a time delayed 100mA RCD, but highlighted it is NOT a requirement of BS7671, unless of course you can advise differently?

Then why would you highlight something like that, that should be a part of every TT system. So what if there is no regulation in your bible, the same bible advocates a numbty 200Ohm Ra for a TT system!!
Can you not think for yourself, does everything have to have a reg attached for you??

An understanding of a TT system coupled with some commonsense, should tell you an S type upfront RCD is a prudent additional protection to any (dual 30mA RCD protected or otherwise) TT system. As i stated before, your comment on the no requirement of a time delayed RCD should not be taken any notice of at all!!
 
but circuits without 30ma protection will still require an upfront 100ma rcd in TT installs.
;-)

No they won't. All you need to ensure is that the maximum permitted Zs for each circuit isn't exceeded. If for example you had a stable Ra value of 150 ohms you would be fine with 300mA RCD protection for all circuits other than those that require additional protection by 30mA RCD.

Hell, if you could guarantee a low enough and stable enough Ra value you wouldn't need RCD protection at all!

I'm just trying to get people to think a bit more about things, I'm not neccessarily advocating ommision of 30mA RCD protection :)
 
No they won't. All you need to ensure is that the maximum permitted Zs for each circuit isn't exceeded.

and what are the chances of getting a Ze/ Ra below 0.5 ohms from a rod to give you a fighting chance of meeting the max Zs of 1.16 for a 32A type b ? none i'd say.


If for example you had a stable Ra value of 150 ohms you would be fine with 300mA RCD protection for all circuits other than those that require additional protection by 30mA RCD.

150 ohms isnt that stable at all , most highways authorities accept no more than 20 , and if that 150 creeps up then that 300ma wont be doing its job , hence the 100ma suggested in the OSG ;-)

Hell, if you could guarantee a low enough and stable enough Ra value you wouldn't need RCD protection at all!
ok.

I'm just trying to get people to think a bit more about things, I'm not neccessarily advocating ommision of 30mA RCD protection :)

...............
 
and what are the chances of getting a Ze/ Ra below 0.5 ohms from a rod to give you a fighting chance of meeting the max Zs of 1.16 for a 32A type b ? none i'd say.

In your average domestic setting the money spent on achieving such a low result would far outweigh the benefits of such a result however in larger installations I'd say it would be quite easy to achieve such a low Ra. Oh, and the max Zs is 1.44. Yes I'm a pedant, what of it?! lol


150 ohms isnt that stable at all , most highways authorities accept no more than 20 , and if that 150 creeps up then that 300ma wont be doing its job

C'mon Biff, you're smarter than that.

Everyone knows that stability has little to do with the size of the Ra value. There are so called 'sparks' up and down the country pi$$ing on rods to achieve low Ra values but does that value do anything for it's stability? No.


but circuits without 30ma protection will still require an upfront 100ma rcd in TT installs
hence the 100ma suggested in the OSG

So is that a requirement or a suggestion? :D


Anyway, you're missing my point entirely. I'm not advising on a solution, I'm not sitting here saying that I would go for a low Ra value just so I can get away with a higher rated RCD?!, I'm not even saying what I would or wouldn't do myself... I'm merely pointing out the common misconception that TT systems need 30mA RCD protection and exposing the misguided link in peoples minds between the phrases 'TT' and '30mA'.
 

Reply to Domestic DB in the Domestic Electrician Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
715
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

  • Question
Thank you so much for that! When I went to do the Ze at the DB, I tripped the RCD in the CU in the house, I understand that's a hard question...
Replies
2
Views
207
You cant just "avoid" the use of RCD's for nuisance tripping... it will depend on how the cable is routed. (ie buried less than 50mm) What has...
Replies
7
Views
380

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top