Kate

hey,

Hoping someone may know more on this than I do. Extractor fan above a shower in an en-suite, in-line fan so unit is up in the loft.
I know you can get condensation and "dripping" from the unit. How bad can this get?

Had a customer ask me to look at why their fan had stopped working. It was only 2 or 3 months old. Jumped up in the loft, removed the duct, could have easily filled up 2 buckets with the amount of water that came out. Travelled from the roof tile, right through the duct (had a drop point here) through the fan unit itself, into the duct on the other side. There was another drop point here which had stopped it from entering back into the shower room!

I may be completely wrong, and tell me if I am. But to me, that's far too much water for condensation surely? I was thinking faulty roof tile as this was existing and many many years old.

IMG_5925.JPG

IMG_5926.JPG
 
You can, as witnessed, get a heck of a lot of water sitting in those flexis. A condensate trap/run off and some insulation would definitely not be a bad idea. As well as either rigid duct or keeping the flexi taut.
Has the roof vent been checked, as that could be letting water in.
 
if the flexi duct is not stretched out it will cause system pressure which means the fan will have to work harder, air travels along the edge if smooth it will not get much resistance & the air will be pushed further.
if the ridges in the flexi duct are closed up the air will not roll along the smooth edge & it will start to fold back on itself creating system pressure this then means the fan unit will have to over come the folding air coming back onto itself, if you can shorten the length of tube by stretching it out that will help. cover in insulation as the hot air & vapour will hit the cold air in loft creating more condense in the pipe work.
best way use as much rigid pipe as you can to replace the flexi duct.
 

Reply to Domestic extractor fan problem/question in the Domestic Electrician Forum area at ElectriciansForums.net

Similar Threads

  • Question
Thanks for your advice guys. very helpful
Replies
4
Views
1K
Thank you. We do have a window. Do you think my idea (even if is adds complexity) is workable? Nothing fundamentally wrong that I am missing?
Replies
6
Views
631
  • Question
I'm familiar with many domestic extractor fans which are primarily class 2 (double insulated) and consequently are not required to be earthed...
Replies
13
Views
2K
  • Question
Rcd protection?
Replies
19
Views
2K
  • Question
Many thanks all for the advise and suggestions. I’ll give the client the option of extractor fans
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks