Hoping someone may know more on this than I do. Extractor fan above a shower in an en-suite, in-line fan so unit is up in the loft.
I know you can get condensation and "dripping" from the unit. How bad can this get?

Had a customer ask me to look at why their fan had stopped working. It was only 2 or 3 months old. Jumped up in the loft, removed the duct, could have easily filled up 2 buckets with the amount of water that came out. Travelled from the roof tile, right through the duct (had a drop point here) through the fan unit itself, into the duct on the other side. There was another drop point here which had stopped it from entering back into the shower room!

I may be completely wrong, and tell me if I am. But to me, that's far too much water for condensation surely? I was thinking faulty roof tile as this was existing and many many years old.

IMG_5925.JPG

IMG_5926.JPG
 
I instantly thought condensation but I was surprised by the sheer amount of water!! Wanted to ask advice before I report back to the customer.
Ducting that's in place is disgusting so I'm picking some up in the am
 
Is there sufficient airflow under the door of the bathroom?

I normally provide an estimate - option A is a like for like , option B is for a far better unit - most people opt for option B
 
Is there sufficient airflow under the door of the bathroom?

I normally provide an estimate - option A is a like for like , option B is for a far better unit - most people opt for option B
This wasn't my job, i didn't install the original fan. Was just asked to look at it when it stopped
 
Original was a manrose one, have the details in the truck. Not sure which model but had some scathing reviews on amazon

There are Manrose and there are Manrose. The one in my link is ten times the unit of the one in your picture. Those are piddly little ones not really suited for purpose.
 
Its building Regs to install insulated ducting inside loft spaces, as the duct itself condenses. Make sure its taught and not sagging or swap it out for 4'' soild.
 
There are Manrose and there are Manrose. The one in my link is ten times the unit of the one in your picture. Those are piddly little ones not really suited for purpose.
Yea I saw! Your link was 240 odd m3/hr. going to message customer and suggest they put a stronger unit in
 
You can, as witnessed, get a heck of a lot of water sitting in those flexis. A condensate trap/run off and some insulation would definitely not be a bad idea. As well as either rigid duct or keeping the flexi taut.
Has the roof vent been checked, as that could be letting water in.
 

Reply to the thread, titled "Domestic extractor fan problem/question" which is posted in Domestic Electrician Forum on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Daily, weekly or monthly email

Back
Top