I have been asked to look into a random tripping RCD.
The installation is quite simple, now only only four circuits,
None RCD protected side has only the lights and a redundant 16A MCB 2.5mm radial for which no accessory could be found, possibly disconnected outside lights but the circuit was still live, this has been disconnected and put in connectors in the CU.
RCD side has a 16A MCB 2.5 radial with only one double socket outlet, a 32A MCB ring doing the majority of the sockets (possibly with a ring off the ring but that's another story), a 20A 2.5mm radial doing living room sockets and finally a 40A MCB 6mm redundant circuit serving a removed shower.
All IRs pass although the 20A radial and 32A ring both had low readings at 2-3MOhms. All other tests pass comfortably.
However the 40A ex-shower circuit still had the Neutral and CPC terminated in the CU, the other end could not be located, probably cut off and plastered in the bathroom wall.
I have disconnected the the Neutral and CPC for the ex-shower and made them safe in terminal blocks in the CU.
After 4 days there have been no more random tripping whilst I've tidied up some loose ends I'm concerned that I haven't really found the fault.
Could a Neutral and CPC buried in a damp wall like this cause an RCD to trip?
Any thoughts welcomed.
The installation is quite simple, now only only four circuits,
None RCD protected side has only the lights and a redundant 16A MCB 2.5mm radial for which no accessory could be found, possibly disconnected outside lights but the circuit was still live, this has been disconnected and put in connectors in the CU.
RCD side has a 16A MCB 2.5 radial with only one double socket outlet, a 32A MCB ring doing the majority of the sockets (possibly with a ring off the ring but that's another story), a 20A 2.5mm radial doing living room sockets and finally a 40A MCB 6mm redundant circuit serving a removed shower.
All IRs pass although the 20A radial and 32A ring both had low readings at 2-3MOhms. All other tests pass comfortably.
However the 40A ex-shower circuit still had the Neutral and CPC terminated in the CU, the other end could not be located, probably cut off and plastered in the bathroom wall.
I have disconnected the the Neutral and CPC for the ex-shower and made them safe in terminal blocks in the CU.
After 4 days there have been no more random tripping whilst I've tidied up some loose ends I'm concerned that I haven't really found the fault.
Could a Neutral and CPC buried in a damp wall like this cause an RCD to trip?
Any thoughts welcomed.