domestic fuseboard

S

switched on

Hi i always come on here just to see what everyone is installing and i think it is a fab website just to see others problems and installs etc. Im installing a 25mm 3 core swa into a domestic property as the dno is in an outbuilding i have installed a switch fuse at the origin but i was wandering if it was ok to use a metal ccu in the house. I cant imagine anything being wrong with this just easier to gland to etc or i suppose i could put a galv box next to it. Just want to get it tip top as hopefully im having my napit inspection on this job. What do you guys suggest or do. Thanks in advance
 
MK's metalclad CU's look just like their insulated ones.....


MK5512.JPG
 
no its still a tncs system as its only 10 metres away but he wanted all the meters outside in a barn basically. Yeah i think thats going to be the option swa into a metal clad mk sentry board. Thanks for your advice
 