The shower being fed from the dp switch?

Its the first time I have come across this and not sure what to make of it. Have any of you lot seen this before?
 
To be pedantic, there is no requirement to 'RCD protect' a shower.

It is the circuit which would nowadays require the RCD protection as, indeed, would any other circuits in a bathroom.

This may have the same outcome but would anyone similarly code the light fitting?
 
Why? Code 3 surely.

I used to go with the code 3 observation for no RCD for a showers but was pulled up by my scam that it should be a code 2 . If there was supplementary bonding I would Code 3 it though , and as stated its the circuits not the appliance that as to be protected any way , I think its a tuff one to call and would no argue with the code 3 if on a report done by others,but would go for a code 2 in most situations if I was doing the test unless you can convince me otherwise.
 
I used to go with the code 3 observation for no RCD for a showers but was pulled up by my scam that it should be a code 2 . If there was supplementary bonding I would Code 3 it though , and as stated its the circuits not the appliance that as to be protected any way , I think its a tuff one to call and would no argue with the code 3 if on a report done by others,but would go for a code 2 in most situations if I was doing the test unless you can convince me otherwise.

Surely if it complies with the regulations it was installed to then it can't warrant a C2 and be potentially dangerous!

What reason did you're scam give for it being a C2 out of interest?
 
They said that if there was earth leakage and no supplementary bonding and you are soaking wet in the shower then the risk of electric shock is higher and use of an RCD would give you the additional protection.
I feel that just because it a new regulation and was not in the 16th it not necessary just a deviation from the regulations and code 3 it ,it down to each installation for example maybe a care home full of venerable people or a rented accommodation where the tenant will use any excuse to say the electrics are unsafe An RCD would be a good idea, were do we draw the line as regs get updated, I know we test the installation to the regs at the time it was installed but surely the regs are updated to improve the safety of the installation and just giving all new reg deviations a code 3 does not seem right.
 
They said that if there was earth leakage and no supplementary bonding and you are soaking wet in the shower then the risk of electric shock is higher and use of an RCD would give you the additional protection.
Well, yes but that's a different matter, isn't it?
Without RCD protection at the time there should have been supplementary bonding so a code 2 would be for the lack of bonding, not lack of RCD.

I feel that just because it a new regulation and was not in the 16th it not necessary just a deviation from the regulations and code 3 it ,it down to each installation for example maybe a care home full of venerable people or a rented accommodation where the tenant will use any excuse to say the electrics are unsafe An RCD would be a good idea, were do we draw the line as regs get updated,
The regs. are rarely retrospective so 'improvement recommended'.

I know we test the installation to the regs at the time
We test to the current regs. and bear in mind the regs at the time of installation.
If it was considered 'safe' at the time it cannot be potentially dangerous now - so improvement recommended.

it was installed but surely the regs are updated to improve the safety of the installation and just giving all new reg deviations a code 3 does not seem right.
Even safer now does not mean it was dangerous.

An old car without seat belts is less safe but is it potentially dangerous?
The car itself will be less safe but is it potentially dangerous?
 
Well, yes but that's a different matter, isn't it?
Without RCD protection at the time there should have been supplementary bonding so a code 2 would be for the lack of bonding, not lack of RCD.


The regs. are rarely retrospective so 'improvement recommended'.


We test to the current regs. and bear in mind the regs at the time of installation.
If it was considered 'safe' at the time it cannot be potentially dangerous now - so improvement recommended.


Even safer now does not mean it was dangerous.

An old car without seat belts is less safe but is it potentially dangerous?
The car itself will be less safe but is it potentially dangerous?
A profound statement
 
All of which proves if you get two reports on the same installation by two different electricians one might be a satisfactory.....and one an unsatisfactory.
Dont inspire confidence does it?

Then one or the other of them has done it wrong. The guidelines are pretty straightforward and simple to follow.

I really do wonder how many people have actually read the guidelines for carrying out an EICR which are part of the model form in bs 7671.
 
The ESC BP guide No 3 says:

Absence of supplementary bonding where required, such as in a location containing abath or shower, where any of the following three conditions are not satisfied:

All final circuits of the location comply withthe requirements of Regulation 411.3.2 forautomatic disconnection, and
All final circuits of the location haveadditional protection by means of a 30 mARCD, and
All extraneous-conductive-parts of thelocation are effectively connected to theprotective equipotential bonding (mainearthing terminal).
 
Last edited:
An old car without seat belts is less safe but is it potentially dangerous?
The car itself will be less safe but is it potentially dangerous?

Yes It hurts when you go through the windscreen

Just out of interest then if you carried out an EICR to a site that was installed to the 17th addition and there was now RCD protection for circuits in a bathroom /shower room would it be a code 2 or 3
 
Last edited:

Reply to Domestic. Has anyone seen this before? in the Domestic Electrician Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Happy Christmas to everybody
    • Friendly
    • Like
Replies
6
Views
257
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
730
  • Sticky
  • Article
Thanks so much for sharing this with us! I’ll definitely take a look, it seems like there are a lot of useful and interesting products. The idea...
    • Like
Replies
5
Views
2K

Similar threads

  • Question
A further update - under floor in front room:
Replies
4
Views
910
  • Question
This controller might do the job if you have single colour strip. You'll still need a power supply prior to this! Lots of additional features you...
Replies
3
Views
275

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top