The wording of
421.1.201 Within domestic (household) premises, consumer units and similar switchgear assemblies shall comply with BS EN 61439-3 and shall:
(i) have their enclosure manufactured from non-combustible material, or
(ii) be enclosed in a cabinet or enclosure constructed of non-combustible material and complying with Regulation 132.12.
NOTE 1: Ferrous metal, e.g. steel, is deemed to be an example of a non-combustible material.
NOTE 2: The implementation date for this regulation is the 1st January 2016, but does not preclude compliance with the regulation prior to that date.
The British Standard; BS EN 61439-3, mentioned in the regulation, is entitled
"Low-voltage switchgear and controlgear assemblies; Part 3: Distribution boards intended to be operated by ordinary persons (DBO)"
The key thing is the regulation says that the type of switchgear they are referring to
SHALL comply with the above BS, so
IF the isolators are covered by the interpretation of:
"consumer units and similar switchgear assemblies" then they'll need to be built to comply with the BS, and not the other way round, (if they don't comply with the BS / built to a different BS, then they're not considered "
consumer units and similar switchgear assemblies")
So I disagree with WHY napit says it doesn't apply to rotary isolatorsm though do agree with the outcome
From Part 2 definitions of Amd3:
Consumer Units: (See below)
Switchgear: An assembly of main and auxilliary swithcing eqipment for operation, regulation, protectionor other control of electrical installations
According to the IET: Consumer units - IET Electrical
Similar switchgear assemblies
The phrase ‘similar switchgear assemblies’ in Regulation 421.1.201 means those assemblies used for the same fundamental application as a consumer unit. A consumer unit is defined in Part 2 of BS 7671:
‘Consumer unit (may also be known as a consumer control unit or electricity control unit). A particular type of distribution board comprising a type-tested co-ordinated assembly for the control and distribution of electrical energy, principally in domestic premises, incorporating manual means of double-pole isolation on the incoming circuit(s) and an assembly of one or more fuses, circuit-breakers, residual current operated devices or signalling and other devices proven during the type-test of the assembly as suitable for such use.’
An example of a similar switchgear assembly is a three phase distribution board that is intended to be operated by ordinary persons. This would have to have isolation that interrupts the three incoming line conductors and the neutral, rather than just double-pole isolation as mentioned in the above definition
.
The key thing hear is that we are dealing with
Part 3 of the BS, which specifically deals with CU's / DB's
Reading the above, I reckon NICEIC have it wrong, and Napit have it right, though for the wrong reason
Qn: Anyone got or seen a copy of BS EN 61439-3:2012 ?