Are you putting in a ring solely for the integrated appliances?When wiring a domestic kitchen is ok to supply integrated appliances from 32A/ 2.5mm ring via 20A D.P. Multi grid Switches , using 2.5mm on out going side of switches to a 1 gang socket or spur ?
Yes, usually those appliances that are designed for EU where the 16A radial is the norm.Some appliance manufacturers specify a 16a over current device.
Do they mind using BS 1363 sockets which only have to cope with 20A in the cable?That’s how a lot of new builds are done. Although I think there’s a few on here who don’t like using 20A DP switches protected by a 32A ocpd.
I don’t know, it’s not something that concerns myself. Have same set up in my house, and I don’t see any issues personally.Do they mind using BS 1363 sockets which only have to cope with 20A in the cable?
Never understood that myself as a standard domestic appliance would never draw anywhere near 20 amps. I think they assume that the DP switch would have 32 amps flowing through it rather than just the supply side terminations taking the current.That’s how a lot of new builds are done. Although I think there’s a few on here who don’t like using 20A DP switches protected by a 32A ocpd.
The plug has a 13 amp fuse in it so that’s not technically accurate, more like the instructions cater for the European 16amp socket arrangement where there is no fuse inside a plug.Some appliance manufacturers specify a 16a over current device. So if you are strictly following the M.I then putting the appliance directly on a 32a ring is not correct.
of course the appliance will work hardwired directly to the 32a ring and I have done this on occasion but technically it’s not correct unless fuses down to the correct rating
The grid switches in many of the late 2000s new build flats I've been in recently all have fusing at the grid switch - but I think when new they had appliance outlet plates at the appliance so no fused plug.20 amp DP switches are used on the grid for isolation/maintenance purposes only, nothing to do with having only 20 amps max through the switch or whatever as installing a fuse or a fused connection unit would be pointless considering the appliance plug has a fuse inside it.
Out of interest, in what circumstance would you not need to use 2.5mm on the outgoing side? And even if you didn't need to, why wouldn't you?And BTW - you don't need to use 2.5mm² on the load side.