Coming across a few installations with no RCD protection. How are folks finding it out there when doing minor alterations / additions to existing lighting circuits with no RCD protection bearing in mind 18th Edition requirements. Appreciate every installation is different. Are folks replacing MCB's with RCBO's, replacing whole CU's or where appropriate using RCD FCU's. Should imagine this is going down well with customers.
 
I have got approval from NAPIT to use devices to BS7288, which relates to RCD sockets and FCUs in a range of situations.

I am not the only one on this forum to have clarified this point by asking my scheme for advice.

No member has reported back that their scheme do not advise on their continued use, that I have seen.

For Christ sake phone your scheme, if you have one, that's what they're there for.

Ooh, I'm getting all unnecessary now, time for a lie down.
In all my years I have never contacted any scheme for advice.
 
In all my years I have never contacted any scheme for advice.

I find it very liberating, sometimes it pays not to over think things and ask the people you pay to do the thinking for you.

I know not all sparks are scheme members so on the available evidence to them your stance is correct.

Good innit.
 
Coming across a few installations with no RCD protection. How are folks finding it out there when doing minor alterations / additions to existing lighting circuits with no RCD protection bearing in mind 18th Edition requirements. Appreciate every installation is different. Are folks replacing MCB's with RCBO's, replacing whole CU's or where appropriate using RCD FCU's. Should imagine this is going down well with customers.
Yes
 
...and be at the mercy of exlisting faults or borrowed neutrals.

Also, and not sure on this as it's additional protection, changing the circuit protection would make you responsible for the rest of it.

No thanks, RCD FCU at spur.
How about an RCD fused spur off an RFC for an outside lighting circuit? An addition to another circuit that in its own right also now requires an RCD?
 
An RCD spur at the origin labelled clearly would be better then hiding a spur in a loft or cupboard and as we need to ensure the whole circuit is protected and satisfactory then cost effective too ?
 

Reply to Domestic Lighting - RCD protection in the Domestic Electrician Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
521
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

No to all. Also would require a means of isolation for PIV - pulling a fuse wouldn't be acceptable. I don't mean to seem disrespectful, but this...
Replies
1
Views
1K
nicebutdim
N
  • Question
ok cheers for the help lads
Replies
7
Views
724

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top