Domestic meter tail isolator | Page 2 | on ElectriciansForums
Discuss Domestic meter tail isolator in the Domestic Electrician Forum area at ElectriciansForums.net
Soulsurfer
Channel Islands
Hey all,
I have a few installs coming up where I need to upgrade cu's and want to install isolators between DNO service head and new consumer units. I have only ever fitted before to twin supply houses on off peak storage heating and was under the impression that a straight enclosure with a 100A DP main switch would be good enough. But DNO have just told me that they also require over-current protection. On two supply i usually use a Hager 4P switch and 2 x 63A MCB's for feed tails but could I use a 100A dp and a separate MCB in enclosure on Brown tail ? or does anyone use easily sourced different equipment?
Thanks,
I don't get how else I'm going to get overcurrent protection without the usual Mcb route as used for comfort heat boards / isolators, spoke to them & they say Mcbs are usual requirement and at 63A. Or should DNO fuse be the only required overcurrent protection ?
I'm thinking an upfront MCB at 63A will not comply fully with 314.
I've just had this on 11 new build houses..for some reason the DNO also wanted over current protection on the tails even though under 3meters etc. couldn't be bothered with the arguments and just wanted them connected so ended up fitting a KMF in each meter box at ÂŁ18 each.
But of course from January we will all love using the Amendment 3 all metal switch fuses!:(
Just a question - but doesn't the lid need to be falling down to comply?
I think that is just another "LAW" that has been made up by schemes and manufacturers to pretend things are the way they say.
As far as I know there is no genuine guidance on downward doors, obviously if you are maintaining a fire barrier then it may be the best approach to ensure that the lid will not be able to remain open. From a practical point of view it is dumb and stupid, oh something has tripped I cannot see through the metal lid so I had better open it, oh I am now holding on to an earthed piece of metal while I put my fingers into a consumer unit that is shaded from the light above so I cannot see if anything is wrong.
On fire retention, this is the idiotic guidance from guidance note four that now explains the intent of the regulation, as opposed to the letter of the regulation, of course anyone who does not have guidance note four will obviously be able to infer this from the lack of any mention of it in the regulation!
This is what GN4 has to say:
3.8.1 Consumer units and similar assemblies in domestic premises
Regulation 421.1.201, which was added to BS 7671:2008 by Amendment No. 3 (2015), requires consumer units and similar switchgear assemblies installed in domestic (household) premises to comply with BS EN 61439-3 and to either:
(a) have their enclosure manufactured from non-combustible material or
(b) be enclosed in a cabinet or enclosure constructed of non-combustible material and complying with Regulation 132.12.
An example of a non-combustible material, according to Note 1 to Regulation 421.1.201, is ferrous metal, such as steel.
The implementation date for Regulation 421.1.201 is 1 January 2016 (six months after Amendment No. 3 comes into effect); see Note 2 to the regulation. However, this does not preclude compliance with the regulation prior to that date.
Where option (b) above is used, it is important that the cabinet or enclosure is suitably selected and erected to meet the requirements of Regulation 132.12. These relate to adequacy of space for initial installation and later replacement individual items equipment, and accessibility of the equipment for operation, inspection, testing, fault detection, maintenance and repair.
The intent of Regulation 421.1.201 is, as far as is reasonably practicable, to contain any fire within the non-combustible enclosure or cabinet and to minimise the emission of flames to the surroundings or into conduits trunking or ducting. Consequently. both of the following are necessary, irrespective of which of options (a) or (b) is adopted.
The non-combustible enclosure or cabinet must provide a complete envelope (e.g. base, cover, door and any components such as hinges, screws and catches) as necessary to maintain fire containment. All blanks, circuit-breakers and other devices must be contained within the non-combustible enclosure or cabinet. The installer must seal all openings into the non-combustible enclosure or cabinet for cables, conduits, trunking or ducting that remain after the installation of cables. Good workmanship and proper materials must be used and account must be taken of the manufacturer's relevant instructions, if any.
The phase 'similar switchgear assemblies' in Regulation 421.1.201 means assemblies used for the same fundamental application as a consumer unit. An example could be a three-phase distribution board intended to be operated by ordinary persons.
Regulation 421.1.201 is intended to apply consumer units and similar switchgear assemblies to BS EN 61439-3 inside all domestic (household) premises, including their integral / attached garages and outbuildings and those in close proximity.
EDIT: Sorry about the tone of the post, I am just really annoyed with this approach, as you may be able to tell!
Reply to Domestic meter tail isolator in the Domestic Electrician Forum area at ElectriciansForums.net
This was posted this week, on topic ....... https://niceic.com/newsletter/omission-of-overload-protection/?dm_i=7G1W,7GCE,K4L2A,WHET,1
I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...