Domestic PIR (TN-S, 60A MAIN, 16MM EARTH, MAIN BONDING 6MM). Neutrals on end to end test at a S/O give zero ohms, Live gives 0.30 ohms & cpc gives 2.7 ohms at same S/O. I'm thinking that if this is a ring then the Neutral is loose somewhere on this cct. Any advice please - i may be overlooking the obvious - (i have measured 230v at all S/O on the cct) - Thanks.
 
Agreed - would get a high reading on Neutrals if loose in the cct. The circuit is supplying some of the S/O in the property and not all - CU has three 2.5 T&E connected for use on S/O (already noted as too many on one protective device). Other ideas?
 
I will isolate the Neutrals on the 3 ccts supplying the rfc's at the CU - what if i still get a zero ohm reading when performing end to end check (I am getting 230V at all sockets) on Neutral conductors for these S/O's.
 
CU has three 2.5 T&E connected for use on S/O (already noted as too many on one protective device).
If you mean that there are three 2.5 T&E on one 30A or 32A protective device, then this may just be the two ends of the ring plus one unfused spur, which is an acceptable circuit arrangement. BRB Appendix 15.
 
Additionally if we are talking 2.5mm twin then the cpc end to end seems pretty high, if line to line is 0.3, would have expected 0.5 ohms or less for cpc, depending on paralel paths.
 
Last edited:
Domestic PIR (TN-S, 60A MAIN, 16MM EARTH, MAIN BONDING 6MM). Neutrals on end to end test at a S/O give zero ohms, Live gives 0.30 ohms & cpc gives 2.7 ohms at same S/O. I'm thinking that if this is a ring then the Neutral is loose somewhere on this cct. Any advice please - i may be overlooking the obvious - (i have measured 230v at all S/O on the cct) - Thanks.

Hello freedomrun - I assume you mean it's open circuit and therefore infinite ohms, not zero. Zero ohms would be quite nice really.

quick and easy way to make it safER would be perhaps to change MCB from 32A (if its this) to 20A. Depends what your remit is as said depends if you are there to fix faults or just report.
 
Simple answer - you got a broken neutral in your circuit - you gotta find where (as already stated - start taking S/O FCU's apart)! Also cpc too high. R1 x 1.67 = cpc. (not taking into account parallel paths).
 
you could split the circuit into two 16a radials which would require disconnecting a leg of the "ring" at a S/O as you have continuity on the live and cpc?

As eddy mentioned your cpc measurement is too high and your max Zs will exceed 1.15 (assuming type B 60898 MCB) So you need to do further investigation and find out what is tapped into the original ring circuit. I would quote for 1 hours testing to investigate the fault which should be enough time to remove all points if required and carry out the remedial work to put the circuit right. Splitting the circuit should be plan B as more often than not, upon investigation, you will find a departure.
 

Reply to domestic PIR no end to end reading on Neutrals in the Domestic Electrician Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
252
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
724
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
696

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top