Domestic PIR (TN-S, 60A MAIN, 16MM EARTH, MAIN BONDING 6MM). Neutrals on end to end test at a S/O give zero ohms, Live gives 0.30 ohms & cpc gives 2.7 ohms at same S/O. I'm thinking that if this is a ring then the Neutral is loose somewhere on this cct. Any advice please - i may be overlooking the obvious - (i have measured 230v at all S/O on the cct) - Thanks.
 
I agree with ezzekiel, finding the broken neutral is a priority if your leaving the cable in circuit.

And I agree with Ezzzekiel too, the point I am making is that dependant on your remit, i.e. what you can and can't or have been paid / asked to do, that might not actually be possible in the real world, in which case a five minute job to make it safer is to downrate the MCB. Maybe then on the two weeks until the job is put right and the fault traced, there is no chance of the cable being overloaded.

It depends on the job. I have for example PIR'd a house and reinstated a few things, and found the lighting circuit on a 40A MCB (wired in 1.5 T+E). The job was NOT for me to go fixing everything and setting the world and his dog to look like a carbon copy of the regs, so I disconnected it, turned it off, took pictures and made damned sure the owner understood why.

That was all. It's all very well saying what must be done, but sometimes it might take 6 months for it to happen. My post was meant to offer a slightly more tactical approach. The strategic would be to clear the fault :carolers:
 
Better clarification now i see the point you are making

But your original reply would appear to the op as leaving on a smaller mcb would suffice

Personally i would choose this option as a temp overnight fix if it was too late in day to repair the break
 

Reply to domestic PIR no end to end reading on Neutrals in the Domestic Electrician Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
707
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top