freedomrun

Domestic PME, have two 2.5mm t&e on a B32 mcb, if this was a ring at sometime then the continuity is broken somewhere and i cannot locate the break. No access to underfloor, no spare ways in the CU, has RCD protection to 30mA. I'm thinking it is not compliant to put two Skt Radial cct's on one breaker even if i downrate to B20? Any advice on what to do here please. Thanks.
 
FIND THE BREAK...!!

power up one leg of ring and make not of outlets on/off that way you can use your continuity tester set to OHMS to find furtherst points away from DB that will hopefully be the end of the "radial" before the break.

disconnect the cables from the 2 end outlets and dink a 20A in the box...!

that way your not energising a wall or a screw!
 
I just thought all circuits had to have individual dedicated over current protection, i would'nt put more than one lighting Radial on a single overcurrent device for instance, but that's why i'm asking for some advice from people with more experience.
 
If i am unable to find the break, lets say it was a JB under the floor or in a ceiling, if both legs of the former ring (if this was ever a ring - have no former paper work to refer to & nothing on CU) are protected by a single MCB, then why refer to a wall or screw being energised?
 
If you have two radial runs from a single MBC/OCPD then it is classified as a single circuit, as you can't have 2 circuits fed from the same protective device. Then the protective device has to be sized to the smallest cable (if for example different conductor sizes are present). You quite often see a mains door bell supply, taken from an existing lighting circuit!!

So if you have 2 X 2.5mm T&E radial runs you will need to replace the 32A MCB with a 20A MCB!! ...lol!!
 
what he's saying basically is that when you have located the break between 2 socket outlets, then these 2 outlets must both have their outgoing cables disconnected so that you are not energising the broken section.
 
Domestic PME, have two 2.5mm t&e on a B32 mcb, if this was a ring at sometime then the continuity is broken somewhere and i cannot locate the break. No access to underfloor, no spare ways in the CU, has RCD protection to 30mA. I'm thinking it is not compliant to put two Skt Radial cct's on one breaker even if i downrate to B20? Any advice on what to do here please. Thanks.

What tests have you done on the ring/radials?
 
I've noted what leg supplies each socket outlet and done a Zs test at each. Done an inspection at each and all connections are secure. As Durham suggests, would i now perform an R2 test with wandering lead to find the furthest point on each leg and disconnect the faulty section from there, check all outlets function correctly and then replace b32 with b20? Thanks.
 
Last edited by a moderator:

Reply to Domestic PME, Radial socket outlet problem in the Domestic Electrician Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
184
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
562
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
516

Similar threads

  • Question
By retired electrician, I mean that I have retained my ticket but no longer do installation work. Thanks for the clarification. I missed that it...
Replies
2
Views
469

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top