domestic question???...

D

danpic

Would a 16 amp MCB be capable for a kitchen ring?? 3x double plugs, 4x 13 amp fuse spurs for the washing machine etc.. and the cooker is on its own mcb...thanks
 
Right... Why are you getting involved in changing breakers if you don't know the difference between a radial and a ring O.o

if it's a 2.5mm ring main then it can sit on a 32amp breaker (without getting technical, size of run etc) if its a 2.5mm radial it can sit on a 20amp...

i really feel awkward helping you with this if you have to go out of your way to purchase the correct breaker :-/
 