Hi,

Apologies if this has been posted before which I expect it has but did a search and couldn't find it. Wabt a bit of information on SPD's in domestic premises when carrying out a consumer unit change. Do we have to recommend they are installed now and if not carry out a risk assessment or are we ok not to carry out a risk assessment as its a single dwelling? Also am I right in thinking its a type. 1 that mounts in a din rail enclosure and if so does anyone have a decent wiring diagram. Did a bit of research but still unclear.

Many thanks
 
Hi,

Apologies if this has been posted before which I expect it has but did a search and couldn't find it. Wabt a bit of information on SPD's in domestic premises when carrying out a consumer unit change. Do we have to recommend they are installed now and if not carry out a risk assessment or are we ok not to carry out a risk assessment as its a single dwelling? Also am I right in thinking its a type. 1 that mounts in a din rail enclosure and if so does anyone have a decent wiring diagram. Did a bit of research but still unclear.

Many thanks
What was the results of your research? Regulation 534.1 Appendix 16 table 534.4.10 and table OSG 3.7.3 refers.
 
It would be a type 2 SPD.
Type 1 SPD’s are used in installations with lightning protection.
It’s a conversation to be had with your customer as they are not mandatory for domestic single dwellings where the losses of equipment are tolerable Where SPD’s are not installed.
Offer it to your customer and if they decline then so be it.
Note it on the EIC
 
No risk assessment for domestic, you fit one or you do not ,based on the equipment it protects.
Wiring diagrams are given in appendix 16 of bs7671 and you can get manufacturers instructions/ diagrams
 
So fed from a breaker then from within the consumer unit. What size breaker? Sorry its just easier to ask on here and get direct responses, appreciate the advice from you all
A type 2 cpc connection must be 6mm2 minimum.
Connections should ideally not exceed 0.5m but must not exceed 1 meter in length ie the live and cpc conductors in total combined.
The ocpd need only provide fault protection.
If on the load side of an rcd the rcd should be an S type with an immunity to surges of 3ka
 
main switch >> 32a MCB
6mm out the load of the 32a MCB and a 6mm out the N bus bar

domestic will be a type 2 SPD at the DB

my interpretations is becuase the total value of the installation will in most if not all cases exceed the cost of what it would cost to install a SPD (an additional ÂŁ60+ odd quid in materials when installing a new DB)

therfore 443.4 is not a get out of free card in my eyes

i see it the only way to get out of not installing a SPD when installing a new DB is doing the risk assessment- but good luck doing that accurately and with confidence
 
main switch >> 32a MCB (need a high integrity board if it dual rcd)
6mm out the load of the 32a MCB and a 6mm out the N bus bar

domestic will be a type 2 SPD at the DB

my interpretations is becuase the total value of the installation will in most if not all cases exceed the cost of what it would cost to install a SPD (an additional ÂŁ60+ odd quid in materials when installing a new DB)

therfore 443.4 is not a get out of free card in my eyes

i see it the only way to get out of not installing a SPD when installing a new DB is doing the risk assessment- but good luck doing that accurately and with confidence
The CRL risk assessment is not applicable to domestic single dwelling units
Fitting one is as you say , is based on an assessment of what it’s protecting and cost.
 

Reply to Domestic SPD's help please in the Domestic Electrician Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
228
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
687
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
641

Similar threads

  • Question
Hi I've nearly completed the 2357 NVQ. I'm just a bit stuck with Permits to work, Planned program of work and method statements. I work in the...
Replies
0
Views
473
  • Question
Jumping on and off jobs can be tough going when you're less than confident as every time you go back it's like a new job. that you know little...
    • Like
2
Replies
15
Views
2K
nicebutdim
N

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top