N
nlbhoy
I've recently 1st and 2nd fixed two new build small houses, the job is due to be signed off
on Wednesday.
There's sprinkler systems fitted in both properties, I've fitted Aico detectors throughout, and
had asked the contractor (who's a friend) what was needed for the sprinkler system, I was told
just to provide a supply, as the DB is right next to the flow switch this could be done easily.
After speaking to the sprinkler guy I've been told I should have interlinked them with the
smoke detectors which makes sense. But, Like I says I was told all I needed to do was provide
a supply.
What are my options here?
Does the sprinkler need to be interlinked with the detectors? it's a very small property, can
the sprinklers have it's own sounder? it's a bit late now to start making holes in finished ceiling
to run new cables etc.
I can't find much info regarding regs for domestic sprinklers, any help/guidance would be
appreciated.
I think with Aico they do wireless so if you have only done twin & E to 1st detector then 3 core & E between you should be able to fit a wireless bass at 1st detector to wireless relay base.
not sure on that one drawing definitely shows a hard wire connection from relay through to the sprinkler head, I would not go down the route of wireless unless you clarify that with the guys/ girls who are installing & commissioning the sprinkler system might bite you in the a...
It was just that in the O.P. states does not want to start making holes in finished houses, it is the sprinkler that sets off smoke alarm sounders and I thought that it was allowed to wire smoke alarms interlink wireless if not Aico would not manufacture them.
I would take that on advice straight from the people who are going to commission the system before they get there, if anything like ours they are nationwide & travelled along way to commission if not ready you will be charged for a revisit.
It would be the line that I would take.
The fact that a domestic install requires sprinklers in the first place suggests that there is a need for a higher standard of fire safety systems than is normal for domestic.
Therefore it wouldn't be sensible to just assume that the normal systems are acceptable, there could be a requirement for it to be all hard wired and not use wireless connections.
just done sprinkler system for new builds, system being commissioned by others but some tight requirements.
1st they required their own board was not happy being on the non RCD side on high integrity board.
2nd from consumer unit to the sprinkler system required FP200 fire alarm cable for power.
3rd Aico smoke alarms wired as normal but with a relay card (input type) on one of the alarms so when interconnected it sends signal.
so we had to install second board just for sprinkler system.
4th we did not know at the time but water pressure for the houses & flats did not have enough pressure so a pump was required also.
Marc with this setup using fp200 etc this again is a water mist system introduced under new EN54 regs. for HMO, nursing homes and hotels. If it ware a sprinkler system, you would require a large reserve water storage tanks, multi pumps and jocky pumps. I would imagine that the system installed is a boxed compressor unit straight off mains water, with pipe work in pvc 20mm and all cabling FP200. A sprinkler system would never be activated by detectors, but a water mist is, as the damage resulting in activation is minimal, and can be cleaned and dry out within hours. unlike the litres of water pumped out by a sprinkler head. Its worth a read up as water mist systems are becoming widely used. They can even be built into kitchen water tapes.
Hi tazz
Only the power supply they said needed to be FP, smoke alarms as normal
Had a word with the sprinkler guy on the phone, he's happy enough with
a standalone sounder for the sprinkler system. I don't need to worry about
getting a cable to one of the smokies.
As of now I have know info or spec sheet for the flow switch etc, I was supposed to get all this info by email but I've never received it.
Anyone any advice on how to connect the flow switch? the switch has 2 sides both have "no" "nc" and "common" volt free connections.
Domestic Sprinkler System Help
Domestic Electrician Forum
Thread Tags
nlbhoy,
marc8,
