Upon doing a consumer unit upgrade + installation test today I came accross an unusal fault. I did all the usual dead tests and everything was fine, but when doing a Zs on the boiler/lighting/ring main circuits they all came back as reverse polarity. The first thing that came to mind was having the tails in the wrong way but the L+N tails were connected correctly from the meter to the DB (i tripple checked this as i have come accross meters which aren't the usual L-N-N-L connections plus i had already carried out a succeddful Ze test). The earth cable to/from the rod gave a great reading of 26 ohms although i admit it had been raining at the time of test. I checked the voltage at the boards main switch with the switch in the Off position and N-E i got a reading of 240v and 0v L-E; I also checked this at the meter, same results.

The strange thing is the fault seemed to fix itself, I didn't do anything other than remove the main fuse and then pop it back in place. Afterwards everything was working/reading fine.

Any ideas why this is as me and a colleague were stumped, dodgy meter maybe? I know it sometimes gives false readings if the batteries run low but they are fine. Any input is appreciated as i literally cant get my head around what happened.
 
I will take a stab in the dark
Poor loose connection on the feed side of the meter live load tail
Shunt coil in the meter in circuit and causing it to show 240 volt on the load neutral
Circuit reverse polarity also because of this
Nothing on Live- earth at the board because of the bad/open connection
Removing and replacing main fuse made the connection functional and all voltage readings and polarity corrected

Remote guessworking
icon7.png
 
The first thing to check is the continuity of your BS1363 test lead set, if the earth lead in the lead is broken or intermittent your meter may interpret this as reverse polarity on TN-S or TT installations. Remember to flex the leads, particularly at stress points, while checking continuity.
 

Reply to domestic TT system strange fault in the Domestic Electrician Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
228
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
687
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
644

Similar threads

Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...
2
Replies
17
Views
767
  • Question
What @Avo Mk8 suggests crossed my mind. Try an IR test at 500v.
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top